if 50hz transformer is required to be run on 50% frequency
what needs to be done???????????
Answers were Sorted based on User's Feedback
Answer / pankaj rajput
It will trip on over fluxing protection, if the protection
is installed.
It's not a wise situation to connect transformer to a lower
frequency with same voltage. The flux induced in core is
directly proportional to voltage & inversly proportional to
frequency. Hence the core will be over heated/over fluxed
and may get damage due to over heat.
The only remedy is reducing the voltage in same ratio.
Is This Answer Correct ? | 31 Yes | 2 No |
Answer / ashokreddyreguri
flux is proportional to E\f or V\f
if the frequency is reduced the ratio V\f will increase so
flux will increase.so to maintain this flux magnetizing
current required will increase.this reduces the no load
power factor , so on load power factor is also reduced.
this also reduces o\p of transformer.so V/f ratio of t/f
must be maintained constant.
as 50% of frequency is applied to maintain constant V/f
input voltage applied must be 50%if rated voltage
Is This Answer Correct ? | 16 Yes | 0 No |
Answer / eeaadil
60 Hz is expensive to generate and safer to operate than 50 Hz
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / abhishek goyal
Xmer is the static device which can produce the voltage in
secondary side WITHOUT CHANGING OF FREQUENCY. (Pl read xmer
principle. NO CHANGE REQUIRED.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / sachin_pawaskar2001
Nothing............only you will get 25hz frequency at out
put.
Is This Answer Correct ? | 0 Yes | 24 No |
how technical is calculated in 11kv line and lt line
I WANT TO INSTALL LIGHTING ARRESTOR ABOVE 20 FEET HEIGHT INDUSTRIAL BUILDING. NOW IT WAS 15 FEET HEIGHT HOW MUCH DISTANCE IT WILL COVER & HOW TO CALCULAT THE DISTANCE COVER BY THE ARRESTOR
what is working process of star delta controlling circuit ?
what is the earthing condition between earth & phase.
I have 4 busbar of 1000 ampere. we use 4 busbar to make 4000 ampere in one phase.my problem is that when we applied 60% load on that then busbar produced high noise.what is the reason of that and how can i minimize that noise.
0 Answers College School Exams Tests,
how does a submersible pump work..?
what is meant by loss of field in a DC motor? how a universal motor works?
why nutral and earthing wire connect with each other in main panel board.
How can you calculate in detail the VA burden of current transformer used for Restricted earth fault protection? Please understand that the CT required here is Class PX or X. Also please show the calculations for knee point vtg, stabilizing resistor, magnetising current.
do we use neutral grounding for resistive balanced load? if we use what happen?
The magnitude of sum of two sinusoidal av voltage is equal to 230 volt.the magnitude of each individual voltage is also equal to 230 volt.what must be the phase difference between voltages?
0 Answers PGVCL Paschim Gujarat Vij Company Limited,
Hello sir, pls send me hpcl technical test papers .i am. Appearing for the exam.