in 50 mw generator if field is open in full load running
condition what happen and for protection which relay used?
Answers were Sorted based on User's Feedback
Usually we are using a loss of excitation rely. Which
always getting a sense from the field excitation circuit
continueslly during the runing condition of Generator.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / a1
I is depend on type of operation-
1) If parrallel with grid/Other generator, than it will
draw reactive power from the Grid/Generator and give active
power to the load. It will work as a Induction Generator.
Reactive power of connected circuit will unbalance.
2) If Generator is running island mode(without any other
source), than terminal voltage of genertor will start to
decrease and current will start to increase. Winding temp.
of Generator and drives will increase.
Under excitation relay provide for this.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / deepak
it run as induction gen & draw excitation power from grid
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / prodip das
It acts as a load, Sensing relay of excitation voltage
Is This Answer Correct ? | 0 Yes | 2 No |
Define what is difference between fuse and breaker?
If anyone would like to know or practice for FEWA papers contact me on mohamedrashad2@hotmail.com Just completed the supervisor exam in April 2021
What is differential relay? How it operates?
HOW GENERATING END VOLTAGE LEVEL (6.6 KV/ 10.5 KV/ 11 KV/ 13.5 KV) DECIDED IN POWER PLANT. ON WHAT FACTORS THE GENERATING END VOLTAGE DECIDED, & WHAT IS THE CALCULATION USED FOR THIS.
why is neccessary Tap changing of power transformer with in a certain time
what is b checks and m checks in diesel generator maintenance?
why write 500v on line tester (Test pen)
Explain the different regions in frequency response?
what is mean by xlpe swa pvc
what is the difference b/w conductor and semicoductor
Safety of dry type transformer
why the NGR (neutral grounding resistor) always OFF during DG off?