in 50 mw generator if field is open in full load running
condition what happen and for protection which relay used?
Answers were Sorted based on User's Feedback
Usually we are using a loss of excitation rely. Which
always getting a sense from the field excitation circuit
continueslly during the runing condition of Generator.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / a1
I is depend on type of operation-
1) If parrallel with grid/Other generator, than it will
draw reactive power from the Grid/Generator and give active
power to the load. It will work as a Induction Generator.
Reactive power of connected circuit will unbalance.
2) If Generator is running island mode(without any other
source), than terminal voltage of genertor will start to
decrease and current will start to increase. Winding temp.
of Generator and drives will increase.
Under excitation relay provide for this.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / deepak
it run as induction gen & draw excitation power from grid
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / prodip das
It acts as a load, Sensing relay of excitation voltage
| Is This Answer Correct ? | 0 Yes | 2 No |
i am going to attaned the engineer (disign)iterview at HAL please give me duid line
Following test should be conducted to find out relative polarity of transformenr terminals A no load test B back to back test C phasing out test D none of above
In pakistan appliances work on 220v at 50hz and in us appliances work on 110v at 60hz what is basic theory to explain it
how to identified power tranfer line is how much KV????
I am new guy as an electrical engr. in a 100MW HFO based power project. I am in operations division. I have noticed from last few days, my supervisor sends the last 24 hours energy generation calculation to my plant manager. I have noticed, he calculated last 24 hour's generated energy differences in KWH then he multiplied it with a multiplying factor 960. for example: total difference =2.685 KWH*960= 2577.6 MWH. but he does not not know what is multiplying factor 960?? can anybody explain it??
why the projects getting loss?
Why Nutral CT rating for Earth Fault Protection of Transformer neutral shall be 20% of Full load Current of Transformer
For a 50MVA (138/69/13.8 KV) transformer, what would be the maximum demand in order not to exceed 80% of its operating capacity.
what is allowed value of zero sequence impedancce of 6.6 kv nuetral earthing transformer ?what is the actual value
in ACB breaker requireding 3200Amps. buscoupler getting OFF mode and again it reset and getting normal position give me a required answer?
Why is the generator rating always in kVA and motor rating in kW?
Utility company give the supply to customer in KVA but bill them for Watt.why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)