What are the various methods for effecive earthing in a
factory in a rocky terrain, where soil resistivity is
extraordinarily high? The usual method of 3 m deep earth
pits is not serving the purpose.
Answers were Sorted based on User's Feedback
Answer / ashish
If Earthing Resistance Value is more than minimum specified
value & one pit can not serving the you have to provide
Three to Four Earthing Pit Which are Interconnected
Together Making The Earthing Mat So The Total Effective
Value Will be Less.
Is This Answer Correct ? | 15 Yes | 3 No |
Answer / joby
here the soil resistivity is high. so mat earthing is provided
Is This Answer Correct ? | 15 Yes | 4 No |
Answer / brian
Import good black soil from some where else,mix it with alot
of salt and charcoal dust, dig atleast 2 pits in a space of
10metres apart.
Let each pit have its own earth mat and burry it wit the
mixture mentioned above ie salt, black soil and charcoal
dust and then bond or interconnect the earth mats wit an
earthwire of ATLEAST 35mm2.
Finally pour alot of water in the pits.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / blake australia
There are some powders which harden (i.e. erico make some I
think). Generally would drill a fairly deep hole. insert
earthing rod and surround with these earthing enhancers.
Try to avoid gell or powder forms of earth enhancer as they
tend to wash away when it rains
Is This Answer Correct ? | 7 Yes | 4 No |
Inverter. converter. Ups.MCB.solar.alternators. motors.
WHY KVAR IMPORTANT WHEN ANY PLANT IS RUNNING ON IT'S OWN POWER PLANT?
What is load boxes ?
why do we have spikes enough to burn electronic boards, when generators are not grounded
present we are having 0.8pf but I want increase it up to 0.99 so what is the formula for it and how can i calculate?
11. As per the theory current doesn’t flows in Neutral, but practically it is not applicable, explain why? 12. How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test? 13. Why the transmission lines are in 11kV, 22kV, 33kv, and why not 10kV, 20kV, 30kV? 14. Why do we generate 3 Phase AC Supply? It is possible to generate 4 Phase and 5 Phase explain it? 15. Explain why the Voltage drop will happen in 3 Phase line? 16. What is the equipment used to control the generator output? 17. What are the factors to be considered during the Synchronization? 18. What should be value of Circuit breaker operating time and tripping time? 19. Why the CT Secondary is rated as 5A generally? 20. At which time Synchronous generator act as a Synchronous Condenser?
What is formula of capacitor for 1-phase power connection.how to improve PF. Suppose I want to connect capacitor in refrigerator to reduce power consumptions.
Hi frnds :) plz tell me that i have 100 KVA 3 phase generator so by thumb rule 100*1.4 = 144 amps and generaly we can operate at 80% load...so it will 144*0.8 =112 amps.... so now i m confused about single phase load.....if we use that generator only for single phase the that 112 amps is total single phase load or i can give 112 amps at red 112 amps at yellow and 112 amps at blue.... i mean that total single phase load that 100 KVA generator will take is 112+112+112=336 amp ??
what is mean by lookup table in microprosser.
What is VFD, and how its work
what is difference between KW,KVA,KVAR? also give me the formula for all the three...
Fire pumps are not used with ELCB control, why ?