How to conduct Magnetic Balance Test, Measurement of
Excitation Current (both on HV- and LV-side) and vector
group on a 1000 KVA distribution transformer. There is a
neutral on HV side.
for magnetic balance test apply the 415 v volt to R phase
then measure Y phase voltage it must be 60 to 80 % of i/p
voltage and B phase should measure around 40 to 20 % of i/p
volatge and when voltage applied to Y phase R & B phase
should read 40 to 60 % of i/p reading. For voltage applied
to B pahse reading should be reverse of first case.
and for measuring excitaation current just give 415 V to
either side H.V or L.V but H.V side prefer and measure
current with clamp meter of all phases.
and for vector group just short the R phase of H.V with r
Phase of L.V
measure voltage as
1R-1Y =
1Y-1B =
1B-1R =
1Y-2y =
1Y-2b =
1B-2b =
1B-2y =
then e.g Dyn11
these condition to fullfill
1Y-2y = 1Y-2b
1B-2y > 1B-2b
Is This Answer Correct ? | 7 Yes | 1 No |