A Generator is in running condition and Rotor earth fault
alarm is coming.How to check on line(i.e in running
condition) whether there is actual earth fault in rotor or
not.

Answers were Sorted based on User's Feedback



A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e..

Answer / kk

Rotor earth relay have 2
stage. One 4 alarm & other 4
trip. One can check the
bridge o/p voltage(mV) &
compare with comissioning
time value.

Is This Answer Correct ?    0 Yes 0 No

A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e..

Answer / bhuvnesh kumawat

rotor earth fault alarm comes only if our carbon brushes
become earthed. it may be at the time of changing carbon
brushes.

Is This Answer Correct ?    1 Yes 3 No

A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e..

Answer / sujeet kumar

we have to check the status of zero sequence relay..
if its not affected then there is not any earth fault

Is This Answer Correct ?    0 Yes 5 No

A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e..

Answer / alok

rotor both side earth fault wire open and check countinuti
with the help of multimeter at rotor both end.but one side
wire who is grounded must be grounded.

Is This Answer Correct ?    2 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

What different between kw and kva. why maser AC in kva.

3 Answers  


What is difference between ON delay and OFF Delay Timer?

7 Answers  


Draw torque - speed curve and load curve of induction motor? mark operating point ?

0 Answers  


In Battery Charger - What is the meaning of End Cell Voltage and Float Voltage.

9 Answers   FLSmidth, Focus, PSEB,


Can you explain about TEE protection scheme?

0 Answers   Voltech,






What is Phase to Phase clearance for 800V System Operating Voltage as per IEC61439

0 Answers  


will there be any problem by recovering slip from single phase induction motors?

0 Answers  


for which possible reasons a motor can fail to start??

4 Answers   CEB, Essar,


why generator is design for lagging P.F(power factor)?

3 Answers   BSES,


how much watts are equal to one unit of energy meter?

9 Answers  


what happens when power factor leads or lags to electical or home appliances

2 Answers  


what is difference between KW,KVA,KVAR? also give me the formula for all the three...

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)