Answer / manish joshi
1. RTD's: Resistance temperature Detectors : used to
measure the winding temperature , PT-100 is used in RTD and
normally 6Nos can be used
2. BTD's: Used to measure the bearing Temperature rise.
Normally 1pc/Bearing
3. DTT's : Dial type thermometeres with contacts/without
contacts alarm trip
4. Space Heater: Used to remove moisture when motor starts
after a very long time where moisure is present in the
surroundings. ratings 240 V 1Ph.
5. SPM Nipples: for vibration monitoring
6. Seperate terminal box for space heater.
| Is This Answer Correct ? | 25 Yes | 0 No |
Answer / pramod_wank
The answer of manish joshi is correct some correction as follows
1. RTD's: Resistance temperature Detectors : used to
measure the winding temperature , PT-100(2mA) is used in RTD
and
normally 6Nos can be used(In each winding 2nos RTD)
2. BTD's: Used to measure the bearing Temperature rise.
Normally 1pc/Bearing (In each side 2RTD used Drive side end
(BE) & non drive side end(NDE))the total 4RTD required
3. DTT's : Dial type thermometeres with contacts/without
contacts alarm trip.(DTT normally used for drive side end &
non Drive side end at max 250v,5A)
4. Space Heater: Used to remove moisture when motor starts
after a very long time where moisure is present in the
surroundings. ratings 240 V 1Ph.
5. SPM Nipples: for vibration monitoring (for drive & Non
Drive Side end)
6.Seperate terminal box for space heater(1ph,240v,300w).
7.Greasing Nipple for Drive & Non drive End.
8.Vibrating Sensor at drive side.
9.Main Terminal box to coonect the supply 415V AC.
10 Neutral terminal Box if required
11.Lifting Hook to lift the motor
12.Earting Bolt as per your electrical system.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / nagaraj .n
insulation tester,test lamp,supply wires,rated type fuse,
( T P D T SUPPLY BOARD breaker.isolator&contactor.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / jagannath_sila
to give the motor with a given ckt we requir as motor
contact module of given rating.
in this module we get ckt
breaker.isolator&contactor.normally the contactor rating is
32 amp.
| Is This Answer Correct ? | 5 Yes | 4 No |
why three phase capacitor takes unbalanced current in capacitor bank?
what is power factor ? how we can calculate the low power factor and amount of capacitor for improve that low factor ?
What is EHT(Abrebiation,Function,Voltage Regulation & how it works?
what purose of the double circuit transmission line phase of the line phase changed for circuit-1 for Circuit-2 R-Y-B B-Y-R
why the value of impedence is taken as %impedence in fault currrent calculation
design of IGBT firing circuit for 11KV
i am going to give the JSEB,RANCHI exam for power plant,so i need some samples of papers related to that,so please send me these papers by my mail id.
what is relation of rpm with Power supply? rpm directly Proposational to power ?
Does all the output contacts (N/O as well as N/C) of a Numerical relay operate when relay receives a binary input/inputs or contacts are designated to specific logic input/inputs and only these contacts operate?
what is the difference between surge arrestor and lightning arrestor ?
how many bulb of 60watt at 300volt is used to maintain 0.25 amp.with valid reason?
no of rotrs poles in salient pole synchronous machine
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)