Why Generator KVA not in KW ?
Answers were Sorted based on User's Feedback
All electrical devices that supply power are usually rated in kVA. but generator put supply power in kVA because KVA is "apparent power" which does not take an account of power factor and KW is "true power". They generated own power factor
like :
VA = E X I
W = E X I COS PHI
Is This Answer Correct ? | 2 Yes | 0 No |
All electrical devices that supply power are usually rated in kVA. This includes transformers, UPS's & the like.
Simply put, the difference between kVA & kW is that kVA is "Apparent Power", which does not take into account the Power Factor & kW is "True Power" . See the below equations:
VA = E x I
W = E x I x Cos phi
The above equations are only for single phase.
When a manufacturer makes a transformer, generator, UPS etc, they have no idea of the type of load that will be used & consequently can only rate the device according to its maximum current output that the conductors can safely carry (at untiy Power Factor) & the insulation rating of the conductors (voltage & temperature).
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / dave mudra
The power √3 VL IL Cos φ delivered by the alternator for the same value of current, depends upon p.f. (Power Factor=Cos φ) of the load. But the alternator conductors are calculated for a definite current and the insulation at magnetic system are designed for a definite voltage independent of p.f. (Cos φ) of the load. For this reason apparent power measured in kVA is regarded as the rated power of the alternator.
Is This Answer Correct ? | 0 Yes | 0 No |
I have a question, I visit 01 site and face a problem, there is 2.5 ton Air Con working, when air con compressor is running at that time rectifier voltages are increasing upto 290-295 v and rectifier is giving main high alarm (rectifier is APC single phase), before starting compressor rectifier voltages was 230v. when air con is going off rectifier voltages are decreasing smoothly at its actual voltages 230v. Load on Genset phases is this: Red-13.5 amp AC (Air Con load), Yellow-1.7 amp AC (BTS lights etc.) and Blew-4 amp AC (telecom system load), Genset phase to phase and neutral to phase voltages are also ok. These are 10 sites having same system and same rectifier APC brand at every site 02 genset are working but the problem is same at all these 10 sites. What will be the reason behind???
Why the frequency of ac in india is 50 hz but in some other countries it is 60 hz.
how do you reduce the skin effect
Advantage of LT panel vs HT panel
How to connect frequency meter in metering circuit?(single phase and three phase frequency meter)
in dc series motor if field wdg is shorted then
Safety devices in SF6 Circuit Breaker?
why we step/down voltage in multipul of 11kv?
I want to merge a cable..in between two metering Cubicals which contains CT's and PT's and Energy meter..before taking merger..what are the common things required?
what is the reactance,capacitance & impedence electrical armoured & unarmored Cables.
what is the use of choke on tube light fitting
37 Answers Bhel, Dharma, HSBC, TCS,
what is Fault level? why it is calculated? how will u decide same for our plant?