Answer / dhiraj shringi
the power upto the fault in power system is known as fault
level power.
it is calculated by the following formula:
fault MVA= BASE MVA/PU IMPEDANCE upto fault level.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mahesh sali
As per IEC std. Low voltage fault have decide as below
mentioned ranges.
For 50 KA / 65 KA at 1 or 3 sec.
for cal Fault current KA - ( KVAsc/ %sub transient
reactance ) *100
thanks
| Is This Answer Correct ? | 0 Yes | 0 No |
1 KW = how many kva
How to select the rating of a CT used for REF protection. The rating can be of equal rating of Phase current or neutral current rating
how to calculate EXCITATION VOLTAGE & CURRENT in ALTERNATOR
what happened if power factor is "1"
what is the working and construction of generator
How can we calculate the resistance of earthing & how can we control it?
purpose of check value
why occ characteristics of generator is also called as magnatization characteristics
How to calculate the total number cells required for a particular KVA UPS system?
what is the abbreviation & meaning of UI charges
Is there thumb rule to calculate how many Insulators to be used for Transmission line of different volatges
what are the disadvantages of low power factor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)