why we are using (-24VDC) and where we r using plz tell me
Answers were Sorted based on User's Feedback
Answer / mugil
In Vibration Monitoring System -24V DC is using to Proximity sensor(Bently Naveda).
Because PNP transistor is used in this proximity sensor.The PNP transistor bsae voltage is negative 24v supply.That's why -24v DC supply is using.
When the probe is in air it will have no induced voltage
so all -24 voltage without induced voltage will return back.
| Is This Answer Correct ? | 8 Yes | 1 No |
-24V DC is used for Telecom server and equipment, as positive terminal is grounded.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / pandu
mugil ji your answer is correct and one thing in plc, is it possible to use -24vdc
| Is This Answer Correct ? | 0 Yes | 0 No |
In telecom Industry, Telecom devices use -24 Volts DC, as positive terminal is grounded.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mugil
Mr.Pandu,
-24V DC You can use in PLC also.Normally Phase and Neutral is using for +24VDC. but in -24 V DC case you should change the connection Phase to ground and Neutral to Phase.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / md. afroz alam
Mugli ji I am confused with your answer using PNP transister or NPN transister tell me pls
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the Relation Between flow and pressure. How both terms related with each other.
HOW TO DO PERFECT CALIBRATION OF DIFFERENTIAL PRESSURE TRANSMITTER FOR CLOSE VESSEL TANK LEVEL PURPOSE ???? AND HOW TO MAKE ZERO PRESSURE ?? Rosemount 2051 Pressure Transmitter with HART® Revision 5 and 7 Selectable Protocol BIENG USED !! HOW TO CALIBRATE FIELD SIDE DPT WITH THE HELP OF SPAN & ZERO PUSH BUTTONS ??
What is the detail function of I/O card in DCS ? Why we dont use the I/O directly with controller?
What is the purpose of MATLAB?
How do you troubleshoot accelerometers used in Vibration monitoring/tripping
what is the working principle of ABB gas analyser of kiln in cement industries
How to do calibration of magnetic flowmeter
I work on a electronic positioner transmitter 4211 at the field.I connect my multimeter in series to get the current output then I calibrate it to 4ma in 0% of position of the valve and 20ma in 100% position of the valve.My problem is in the field I get the correct output current based on my multimeter but in the dcs they only receive 40% in a output 20ma of this positioner.Then I try to simulate in this analog card and they receive the equivalent percent on the value that I simulated.Is ther any possibility to reset the zero and span of this positioner 4211 fisher.And what other possibility I can do to fixed this.This is my email add ( landicho_randy@yahoo.com )
How can SmartPlant Instrumentation users take advantage of these global services?
1)why we are using mostly Ultrasonic Flow meters to measure flow, rather than Radar waves? 2)why we are using Ultrasonic waves and Radar waves to measure the Level?
give some question relative instrument fitter?
In control valve , Failure position : Close If it is Fail close(FC) during failure of AIR.. what will be the initial/ normal position of control valve is it normally open or close? please some one explain soon..
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)