What are Line losses and how can be it minimized/controlled.?
Answers were Sorted based on User's Feedback
Answer / rk
T&D Losses= (Energy Input to feeder(Kwh)-Billed Energy to Consumer(Kwh)) / Energy Input kwh x100
Distribution Sector considered as the weakest link in the entire power sector. Transmission Losses is approximate 17% while Distribution Losses is approximate 50%.
There are two types of Transmission and Distribution Losses
Technical Losses
Non Technical Losses (Commercial Losses)
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / abc
There typically two types of losses in line T&D.
1. Technical Losses
The technical losses are due to energy dissipated in the conductors, equipment used for transmission line, transformer, subtransmission line and distribution line and magnetic losses in transformers.
Technical losses are normally 22.5%, and directly depend on the network characteristics and the mode of operation.
The major amount of losses in a power system is in primary and secondary distribution lines. While transmission and sub-transmission lines account for only about 30% of the total losses. Therefore the primary and secondary distribution systems must be properly planned to ensure within limits.
The unexpected load increase was reflected in the increase of technical losses above the normal level
Losses are inherent to the distribution of electricity and cannot be eliminated.
There are two Type of Technical Losses.
1. Permanent / Fixed Technical losses
Fixed losses do not vary according to current. These losses take the form of heat and noise and occur as long as a transformer is energized
Between 1/4 and 1/3 of technical losses on distribution networks are fixed losses. Fixed losses on a network can be influenced in the ways set out below
Corona Losses
Leakage Current Losses
Dielectric Losses
Open-circuit Losses
Losses caused by continuous load of measuring elements
Losses caused by continuous load of control elements
2. Variable Technical losses
Variable losses vary with the amount of electricity distributed and are, more precisely, proportional to the square of the current. Consequently, a 1% increase in current leads to an increase in losses of more than 1%.
Between 2/3 and 3/4 of technical (or physical) losses on distribution networks are variable Losses.
By increasing the cross sectional area of lines and cables for a given load, losses will fall. This leads to a direct trade-off between cost of losses and cost of capital expenditure. It has been suggested that optimal average utilization rate on a distribution network that considers the cost of losses in its design could be as low as 30 per cent.
Joule losses in lines in each voltage level
Impedance losses
Losses caused by contact resistance.
Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate the input current in singel phase and 3phase supply to 5kva ups
what is meant by k-rating in isolation transformer?what is k9, k14 stands for?
Why arc quenching is used in Diode ?
Can anybody tell me what the breakdown voltage is for air and what it is for transformer oil please?
What will happen 50 HZ motor when you will give 60 HZ?
7 Answers Bhushan Power Steel,
why v use only sodium bulb or orange color lights on streets, y nt CLF OR TUBE LIGHTS
Is there possible to Test Transformer for Overfluxing Capability. Or is there any firm who does Overfluxing Test on Transformer?
why causes the burnt of AC Electrical Motor ?
can we connect both delta and star to the transformer secondary and for what reason?
Which rccb 30ma,100ma,300ma sensitivity should be used in domestic line and what is difference, advantage and disadvantage of all three
what happens when the phase and earth wires comes in contact? and why