how a circuit breakers work at fault condition .plz give a specified answer.
Answer / jithendra
circuit breakers works mainly for protection of circuit
so it needed to trip when fault occurs
inside the breakers current transformers (CT's) are placed for sensing the fault
Breaker are operated with closing,triping,shunttrip & Under&over voltage coils
Through ct's fault will sense then pulse will be given to
the triping coil at that time breaker will trip
Breaker will have these faults protections
OVER LOAD
EARTH FAULT
INSTANTANEOUS CURRENT
SHORT CIRCUIT CURRENT
Is This Answer Correct ? | 3 Yes | 0 No |
1]how the voltages and frequency are achieved on ships. 2]how does the line and phase voltages are related on ships.
Why a starter is used for a motor?
50 Answers L&T, Nilachal Polytechnic,
WHEN I AM CONNECTIN TWO ELCB IN PARALLEL.ONE ELCB TRIPPED...HOW IT HAPPEND??
If one d.g. is unable to take full load of system, then second d.g. will take care of partly Load.for this condition RPM of both DG set should be equal.By using Synchronization panel RPM of dg sets are match, is it true?
I am a electrical engg. diploma holder,applied for junior engineer (electrical),Kolkata RRB. Have I to attend all electrical,mechanical&civil portion in written exam.???
Is there any local or International standards that prohibit the installation of earthing pit in the planters area where the earthing pit is subject to continues soak in water?
Why you are switching off arc protection mcb when you are taking shutdown for lv board.
What are the causes of eddy current losses?
We have 90mX100m hangar with 16 no.of supporting pillar. It is required to provide power supply on all pillars. what is suggested earthing scheme for hangars.
how we masure a cuurrent?
what is the relation between currebt & voltage.
What kind of socket shall be provided for window type air conditioner with cooling capacity upto 18000 BTU/hr