We are using 4 MVA transformer and we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral, can we connect separate body earthing pit to other earthing pit (Equipment earthing)?
Answer / riaz abbasi
No, we can not connect equipment earthing with body earthing because in case of earth fault , current will also run in the body via equipment earthing system and will damage other equipments which are installed over the Transformer.
Is This Answer Correct ? | 3 Yes | 0 No |
what are the functions & ratings of panels mentioned below: 1. Main LT Panel(MLTP) 2. Motor Control Centre(MCC) 3.Feeder pillars 4.Busducts
why Current is lead 90 degree and voltage is lag 90 degree in a capacitor.? why Current is lag 90 degree and voltage is lead 90 degree in an inductor.?
How does PLC work for sychronising of Two or more DG sets?
In Power Line Communication (PLC) the wave trap is used to block communication signals from entering neighboring lines. My question is this: Why do they allow for different filtering arrangements on these wave traps? Isn't it always going to be a low pass filter since we want the power frequency to go through, and the comm signal blocked?
What is the difference between LT CT & HT CT?Can we use indoor type transformer as an outdoor type or vice versa?
how to choose the cable rating for load (KW)? EXAMPLE.50KW load
14 Answers ACC, NCUI, Polycab, PowerSol, Siemens, SW,
What kind of preventive maintenance are there for AC induction motor?
HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD EVEN AFTER IT IS DE ENERGISED
Why C.T secondary s2 done earthing?
Please brief me about number of pole in alternator.In single phase alternator coils are connected in star or series. How to calculate frequency for the same.
If a 3 phase induction motor is in off condition in the conveyor and rotor of the motor keeps moving with the conveyor than the resistance of windings of motor varies. why is it so ??
what is the use of capacitor bands?