We are using 4 MVA transformer and we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral, can we connect separate body earthing pit to other earthing pit (Equipment earthing)?
Answer / riaz abbasi
No, we can not connect equipment earthing with body earthing because in case of earth fault , current will also run in the body via equipment earthing system and will damage other equipments which are installed over the Transformer.
| Is This Answer Correct ? | 3 Yes | 0 No |
what is the difference between NC & CNC machine.what is the difference between equipment & machine tool
How one may guess the direction from which the distribution line is incoming if there is no pole plate on poles?
How we can design a cable for a 3phase load.
How can we increase the capacity of Energy.?
do we need NGR panel when the output of the genset is LV but after that it is step up to 22 kv. condition is 12 genset 400v are operating in parallel.
If i have two 3000 kW motors and the whole facility requires a 10 MVA transformer. What would be better installing two 5 MVA transformers(one for 1 motor ) or just a single 10 MVA transformer for both of them. Give reasons for your answer.
what is RFCT and Insulgard Relay & It's function?
what is induction relay
What is signal flow graph?
what is differentila pilot supervision in the incomer control panel in the power station?
why we use star connection in HT motor? and delta connection in LT motor
what is power factor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)