why we use star connection in HT motor? and delta connection
in LT motor
Answers were Sorted based on User's Feedback
Answer / vinoth
In HT motors it will reduce the starting current up to 60 percent thats why we prefer star to delta conection..........but in LT motors we use Direct online starter/.......it doesnt reduce the starting current
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / madhu
The starting current for motors is 6 to 7 times full load current. So start-up power will be large if HT motors are delta connected. It may cause instability (voltage dip) in case small Power system. In starred HT motor starting current will be less compared to delta connected motor. So starting power is reduced. Starting torque will also be reduced. (It will not be a problem as motors are of high capacity.)
| Is This Answer Correct ? | 0 Yes | 0 No |
why leading pf indicates a negative sign???
Hi frnds :) plz tell me that i have 100 KVA 3 phase generator so by thumb rule 100*1.4 = 144 amps and generaly we can operate at 80% load...so it will 144*0.8 =112 amps.... so now i m confused about single phase load.....if we use that generator only for single phase the that 112 amps is total single phase load or i can give 112 amps at red 112 amps at yellow and 112 amps at blue.... i mean that total single phase load that 100 KVA generator will take is 112+112+112=336 amp ??
how to calculate the MF in meter reading
Why did call copper as a electrical conductor?
what is the size(sq.mm) of these conductors dog,rabbit,tiger,panther,mush,
Q.1:What protection will be used on HT and LT side of 33/0.4 KV, MVA transformer. Indicate capacities of protective device to be used. Q.2:Which types of back-up protections are used in the power transformers? What do you understand by the term over travel in the relay? Q.3:How star and delta connected winding transformer are provided from earth fault
What happens to an electric motor if it has poor or no ventilation. Will it burn out? If it will, how long it will run before it burn out?
HOW TO DO GRID EARTHING IN INDUSTRIES FOR A PRODUCTION BUILDING
why only 26v dc is used in aircraft and 115v ac in aircraft.
how we can calculate cable size of 230v,1 hp single phase motor ? panel to motor distance is 25 meter
How to convert a two phase power into a three phase power in induction machine?
what is the voltage and ampere rating of all range of HT conductor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)