what is the acceptable insulation resistance for motor/transformer?
Answers were Sorted based on User's Feedback
A very significant maintenance procedure for checking out the working condition of an electrical system is called IR test or Insulation resistance. It can be said that ht system or equipment is fine when insulation resistance is high.
Megger is an insulation resistance measurement tools for finding the equipment’s insulation resistance. Let us see how is the IR calculated? for more : http://crbtech.in/Electrical-Training/index.php/2017/07/31/define-insulation-resistance-and-its-calculation/
Define Insulation resistance
There is an application of direct current (DC) and not alternating current (AC) and this is the first thing while doing the Insulation resistance test.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / gajendra singh
Insulation resistance tests are made to determine insulation resistance from individual windings to ground or between individual windings. Insulation resistance tests are commonly measured directly in megohms or may be calculated from measurements of applied voltage and leakage current.
Is This Answer Correct ? | 2 Yes | 3 No |
What will be the size of copper cable (each for 3 phase and 1 neutral) from Service connection Kit-Kat to Panel Board (i.e. to main switch) for a 6 pole 3-phase AC induction motor of 200 H.P. capacity? Amp-255 A, Frequency:- 1450 rpm.
What is the function of pulse transformer?
Which type of power plant is more easier to produce electrical power at economical condition?
Why dont we get shock while testing for voltage with a line tester? How the bulb inside the tester glows while testing with tester coz we are totaly isolated from earth or we are not giving close path for the current to flow?
What is pi controller?
Can HT cable(11kv cable) be used for 415V, 700A requirement.
What is the difference between a verilog task and a verilog function?
Why High voltage are generate noise ?
whenever any squirrel or a crow falls on the transformer input line then there is a big explosion and 440 volts of power is being discharged through the neutral line due to which appliances in off mode are also burned.we have earthing for the transformer as well as the bus bar chamber.why is it happening?
How To Convert Apparent Into Real Power Without Knowing Reactive Power?
pls send me some of the solved question booklet of Junior Engineer -2 (ELE) in RRB
I want single line diagram for AMF & DG syncronizing panel