Hai friends I have dought for O2 analyser how to working in boiler area. And what is the basic principles
Answers were Sorted based on User's Feedback
Answer / rambalaji
1. zirconia oxygen analyzers determine oxygen concentration using the conductivity of a zirconia ceramic cell. Zirconia ceramic cells only allow oxygen ions to pass through at high temperatures (750oC). With reference gas on one side and sample gas on the other, oxygen ions move from the side with the highest concentration of oxygen to that with the lowest concentration. The movement of ions generates an EMF (Electro Motive Force) which can be measured to determine the oxygen content
2. The sensor does not actually measure oxygen concentration, but rather the difference between the amount of oxygen in the flue gas and the amount of oxygen in the air. Rich mixture causes an oxygen demand. this demand Causes high voltage to build up due to transportation of oxygen ions through the sensor layer. Lean mixture causes low voltage since there is oxygen Excess. Sensor working in Nernst Principle
In flue gas side O2 is low : High Voltage
In flue gas side O2 is high : Low Voltage
High Concentration : O2 + 4 e 2O2 -
Low Concentration : 2O2 - O2 + 4 e
0% O2 = 0.82 mv
5% O2 = 0.40 mv
21% O2 = 0 mv
| Is This Answer Correct ? | 4 Yes | 0 No |
. When temperature increases the content of oxygen decreases.- principle.
Reference gas(span gas) instrument air 21% O2.
1% gas should provide from cylinder for cal purpose.
| Is This Answer Correct ? | 3 Yes | 1 No |
Hi i am aneesh, done btech in applied electronics & instrumentatiin. And then i took mba in finance & marketing.After that i got placement in finance co and worked there for 3.5 yrs.Now i wanted to come back to engineering job.But without engg experience, i may not able to find an opening.i have done a course related to flow meters and ite calibrations. Kindly suggest where should i try to get a job?
Q- voltage source of 12v is driving the circuit.if circut draw the current of 0.5A them source voltage will became 11.8v.what is the power dilevered by source when circuit draw 5A current ?
Derive capacitance to 4-20ma conversion formula / relation in capacitance type pressure sensor?
why we use sensing type(NPN)on a vibration monitring system not a (PNP)sensing type
how to test rotor &stator earth fault in turbine
Draw a great bridge circuit.
is manifold required for an integral orifice meter?
suppose in dcs range of a flow transmitter is 10t/hr what is dp for 50% in 2500mmwc
what is cascade system ?
when the instrument tapping on pipe line is located below and transmitter is located above the tapping point for liquid service transmitter, what should we do, is there any additional drain valve is required??
difference between DCS @ SCADA system? and how can use in field
in differential pressure transmitter,min&max pressure range for hp&lp
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)