Answer / abdul
It depends on the how much the power factor has to be improved
simple calculation would be
Kvar = KW [tan (cos inverse (old pf) - tan (cos inverse (new required pf)
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / girish
KVAR=KWX0.541(Power factor improvement at 0.98)
KW=20
KVAR=20X0.541
10KVAR
2.5KVAR 4 Steps
| Is This Answer Correct ? | 0 Yes | 1 No |
what is difference between ELCB, RCBO & MCB
What is the difference between a fuse and a breaker?
Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required
9 Answers Emerson, Rajshree Sugars, Siemens,
Differentiate between kirchhoff’s first law and kirchhoff’s second law?
i have seen one 8.4 MW synchronous motor in a plant located in bellary it is fixed with brushless rotary rectifier ,anybody can explain its start up principle
why does the magnetic balance tests at transformer?
What should be cable size for 75KVA 380/220 3ph transformer
in dc shunt motor if field winding is shorted then
How to increase the specific gravity of DG batteries?
Why are the HV motors are connected in star connection?
What are the effects to a distribution transformer rated 10Kv with ratio 10Kv/0.433Kv, 3phase 50hz for example but fed with power supply of 11Kv?
What is the meaning of HT Trivector Meter ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)