Answer / aditya
over frequency occurs when the RPM of prime mover goes above the rated speed. This protection is basically for prime mover and gives a trip signal to the prime mover in case of overspeed so that the centrifugal forces dont damage the prime mover and alternator rotor. This is generally a result of faulty speed governor or sudden throw off or throw in of large magnitude. In addition overspeeding will also result in increase of supply frequency. certian electronic equipments are very sensitive to freq and get damaged hence over freq protection is given.
Is This Answer Correct ? | 4 Yes | 0 No |
FOR 16/20 MVA 132/33 KV ONAN/ONAF TYPE TRANSFORMER IT IS DESIGNED FOR 16 MVA WITH ONAN CONDITION.IT BECOMES 20 MVA UNDER ONAF CONDITION.LOAD LOSS IS GUARANTEED FOR 65KW AT 20 MVA AND % IMPEDANCE 13.75. PLEASE TELL US AT WHAT LOAD LOSS AND % IMPEDANCE IT SHOULD BE DESIGNED FOR 16 MVA AND WHAT WILL BE ITS EFFICIENCY AT 20 MVA?