15 kva dg set single phase takes 63amp( approximate) while same rating 15kva three phase takes 35amp approximate. why ?
and what will be per phase current for 15 kva
Answers were Sorted based on User's Feedback
Answer / h s sandhu
In case of 15 KVA single phase dg set ,the current shall be 37amp while in case of 3 phase 15 KVA the current shall be 22Amp . It is a simle case of formula used for power P=VXI
Is This Answer Correct ? | 0 Yes | 0 No |
why the check zone and main zone are used for Busbar Protn. scheem?
working of diesel generator ?
How to measure the Harmonic Distortion of UPS ie THD?
What is a roll of a adopter pannel in buscoupler pannel????
Why we use parllel operation of alternator
1) What is difference b/w impedence relay and differential relay? 2) what are substations equipments? 3) what is difference b/w circuit breaker and isolator? 4)what are the types of circuit breakers? 5) which medium is mostlty used in circuit breakers and why it is used?
What is the difference between CT for protection and Ct for metering?
what is the function of Moulded case circuit breaker, why it is called Moulded?
UPS battery Back time = no.of Batteries * Ah of the Battery / output KVA * 130 ? what is the 130 means ? can any one help? because all are using this formula how its came 130?
in 33kv line how much current will be
we r having 3 core 3 1/2, 4 core cables how we can know this cable has to be used for this purpose?
testing of Vector Group – YNaoD II