Guy's need your support,I want to measure closed tank level which is under vacuum -630mmHg using DP Transmitter, tank fluid density 1.38, Tank height is 7ft
Answers were Sorted based on User's Feedback
In such case vaccume will apply in both lags equally .
Now hight is 7 ft and density 1.38
7 ft is equal to 84 inches
So ,
84 X 1.38 = 115.92 inches of H2O became our span.
1 inches of H2O = 1.87 mmHg
Thus,
115.92 inches H2O = 216mmHg
tank is closed thats why ,
LRV = - 216 mmHg
URV = 0 mmHg
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / sr
mothods of measurements don't change with change in line pressures ... the methods r same for both +ve and -ve pressure .... in vacuum u just have to take care that vacuum shud not break ....
| Is This Answer Correct ? | 1 Yes | 0 No |
A differential pressure transmitter is required to correct for vacuum pressure. The DP's low side is installed high up, tapped into the vacuum and the DP's high side tapped in near the bottom.
The DP transmitter's minimum range (LRV) is zero
The DP transmitter's maximum range (URV) is:
maximum level height (inches or mm) * specific gravity
Liquid level = measured pressure in water column units (inches or mm) / specific gravity
Many digital indicators just scale the 4-20mA to the desired level range; so a calculation involving specific gravity isn't needed.
For example:
4.0 mA = 0.0 inches level
20.0 mA = 84.0 inches level
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 4 No |
What is the Difference between CNC and PLC
working principle of lvdt?
what is three element loop
where can we use viberation transmitter,and how can we control viberation?
what is the difference about HART, and 4-20mA signal?
i have 20 kw motor & my vfd drive capcity is 18 kw if possible to use 20kw motor on this vfd?
what is an ambient temperature?
How ejector(or)evactor air pump is working in thermal power plant?
Area classification, Equipments, Gas groups, temperature classification, Ingress protection, Fire Extinguishers.
which is type of thermocouple is used to measure 1000deg?
What is a snubber circuit?
If a warning lamp will operate with the ground circuit is bypassed with a jumper wire to ground, what should you check?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)