what are the difference between conventional and smart transmitter.
Answer / carl_ellis
Smart vs Conventional transmitters
Conventional
A conventional 4-20ma transmitter regulates the loop
current and provides only a process variable signal.
The zero and span adjustments are analog adjustments. n
the case of fixed range transmitters the zero and span
adjustments are limited to about plus/minus 2-3% of the
fixed zero or span values. Some conventional transmitters
have an adjustable turndown range, but calibrating a
turndown range requires a simulated process variable (an
applied calibration pressure or a simulated temperature
(RTD or thermocouple) electrical signal). Turndown is
generally limited to about 5:1 or 6:1.
Smart
A smart transmitter provides a process signal but can also
send/receive information about the instrument itself, e.g.
zero and span info, tag (instrument loop identification),
diagnostics, or even multiple process variables using a
digital protocol.
Configuration changes are done either with a keypad and
display or through a protocol like HART, which is
superimposed on the 4-20mA signal, so no additional wiring
is needed for smart communication. HART communication is
accomplished with a handheld communicator or a modem and
software.
Turndown rangeability can be as high as 100:1 (with reduced
accuracy at the low end); 15:1 or 20:1 with stated accuracy
and can be accomplished without applying an external
calibration signal, reference or supply.
Smart transmitters can communicate via a Fieldbus,
Foundation Fieldbus or Profibus.
Carl Ellis
Measure First
Is This Answer Correct ? | 20 Yes | 4 No |
what is the function of boiler in plant?
where do you give the 4-20 ma i/p in a MIL control valve?
define optical temperature detector
How RAL(Rotary air lock)works in cement industry?
How servomotor controls throttle valve of TURBINE?
how many mmwc are eual to 1kg/sq.cm & can we calculate mmwc into tph?
Explain about the leakage class of the control valves
what is the input of conductivity sensor and meter during the calibration time and what is the output?
why Fahrenheit unit of moistur analyzer transmitter
what is the difference between signal cable and ontrol cable?
units of pressure,flow, level,temperature? principle of pressure gauge? calibration of pressure tx., level tx., temperature tx.flow tx.? description of two wire ,three wire and four wire R.T.D.? WHAT IS INPUT AND OUTPUT OF TX.? WHAT IS INPUT AND OUTPUT OF R.T.D. AND THERMOCOUPLE? WHAT IS HOT LOOP AND COLD LOOP? WHAT IS INPUT AND OUT PUT AND OUTPUT OF D.C.S. AND P.L.C.? PRINCIPLE AND WORKING OF HART? WHAT IS PNP AND NPN PROXY? CALIBRATION OF PRESSURE ,LEVEL ,FLOW SWITCH? DESCRIPTION OF FIELDBUS FOUNDATION? WORKING OF SOV.?
What is the maximum distance limit of 4-20mA and 0-10V DC standard signal transmission ?