what are the difference between conventional and smart transmitter.
Answer / carl_ellis
Smart vs Conventional transmitters
Conventional
A conventional 4-20ma transmitter regulates the loop
current and provides only a process variable signal.
The zero and span adjustments are analog adjustments. n
the case of fixed range transmitters the zero and span
adjustments are limited to about plus/minus 2-3% of the
fixed zero or span values. Some conventional transmitters
have an adjustable turndown range, but calibrating a
turndown range requires a simulated process variable (an
applied calibration pressure or a simulated temperature
(RTD or thermocouple) electrical signal). Turndown is
generally limited to about 5:1 or 6:1.
Smart
A smart transmitter provides a process signal but can also
send/receive information about the instrument itself, e.g.
zero and span info, tag (instrument loop identification),
diagnostics, or even multiple process variables using a
digital protocol.
Configuration changes are done either with a keypad and
display or through a protocol like HART, which is
superimposed on the 4-20mA signal, so no additional wiring
is needed for smart communication. HART communication is
accomplished with a handheld communicator or a modem and
software.
Turndown rangeability can be as high as 100:1 (with reduced
accuracy at the low end); 15:1 or 20:1 with stated accuracy
and can be accomplished without applying an external
calibration signal, reference or supply.
Smart transmitters can communicate via a Fieldbus,
Foundation Fieldbus or Profibus.
Carl Ellis
Measure First
| Is This Answer Correct ? | 20 Yes | 4 No |
How do you calibration D.P transmitter? ?
What is instrumentation control?
What is the difference between fiber optic cable & Ethernet cable
2 Answers BEMCO, CCC, Pidilite,
what is the difference betwwen the 2wire level transmitter and 4wire level transmitter??and their applications also??
what is the imbustion control loop
What is exact difference between the panel earthing and system earthing in DCS system. What is the value of resistence.
There is a problem with our HART475 it is not communicating with smart devices error becomes "NO DEVICE FOUND"we have insert 250ohm resistance as per requirement but invain plz tell me the solution?
How does electro magnetic pump works ?
What is scale factor of proximitor & unit of the viabration.
Dear all... I have 1 0-400 duplex type RTD, I connected the A side to the temperature indicator and B side to the PLC panel, but when I have observed then found that The PLC side temp has the variation. and it was distub to other RTD temp also. so what can I do.
Operational amplifiers
Reason for capillary type dp level transmitter fluctuation
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)