How to adjust the zero & span of a control valve from the
posiitioner(MIL)?
Answer / ashish b. patel
when you are open the positioner there are two setting, zero & span. positioner to give 4 mA and set the Zero adjust and valve should be 0% open. after give 20 mA and set to span and valve should be 100% open. this to adjust are very important. after you can give again 4 mA- 0%, 8 mA- 25%, 12 mA- 50%, 16 mA- 75%, 20 mA-100%.
Is This Answer Correct ? | 9 Yes | 0 No |
What information needs for Control Valve "sizing"
What is the difference between floating and fixed voltage?
What is an instrumentation amplifier? How is it better than a differential amplifier when handling outputs from a wheatstone's bridge?
Can I route 110 VDC and 24 VDC in a same Duct for our Interposing relay cabinet? IF yes or NO Please provide me IEEE Std. for the same. Please i required it on Urgent basis, i need to design IRP Cabinets and we have MCC 110VDC and Our Coil side is 24VDC, Please help as soon as possible.
Explain PID, ON/OFF, Controls
0 Answers CCIE, Gulf Engineering,
if i change range of flow transmitter in th field then does it need to change range in dcs?
Which type of pressure can be measured by primary elements?
In close vessel/ drum why we use d.p. transmitter of -ve range i.e. (-)500 to 0 mmwc.
ABB DCS (AC 800 M)redundency take howmany milliseconds to switch from master controller to slave?should be less than DCS scanning time?
what are the possible reasons if a control valve fails to open/close?
what is meaning of static pressure
Hi, am aniket, I got engineering degree in instrumentation and control, but as their were no job availabilities for engineer's post I started working as instrumentation technician I kuwait, so my question is is this technician's experience worth for getting the position of engineer?
1 Answers Almeer Technical Services,