If we know the load for generator in KW then how it will be
change to amps and also if we know the load in amps how it
will change in KW and what Generator is good for
that...suppose load is 500 amps 3phase......??
Answer / ram t shelke
Techanically speaking , Generator is a DC machine i.e an
machine used to supply DC power.but you are saying that it
is a 3phase machine . so you might be talking about
alternator.
if you know the value of generator current , it can be
expressed in terms of KW provided one should know the
terminal or O/P voltage of generator.use following equation
for the required convertion.
KW = 3* TERMINAL VOLTAGE per phase (V) * RATED CURRENT
per phase (A) * power factor/1000
On the other hand , if you know KW out put, one can
calculate corresponding current by following equation
current per phase(A) = kw rating*1000/ 3* voltage per phase
(V)* power factor
Is This Answer Correct ? | 0 Yes | 0 No |
What is the meaning of C1, C61, C91 cable
what u meant by shock ? whether it depends on voltage or current
active elements are those which are capable of
how i calculate the syncrones generator NGR resistance .if we have a 6mw generator line voltage of generator 11kv also line current 393.3 ampere.
Why DG self motor winding burnt out?
if in 3-phase system voltage=440V,frequency=60Hz, current=400A. then if it is single phase then current=? and if it is single phasing then current=?
IN MY SYSTEM THERE IS ONLY OVER CURRENT EARTH FAULT RELAY IS AVAILABLE. FOR THE UNBALANCE SENSING IS THERE ANY RELAY IS AVAILABLE? THE SAME CTs WHICH ARE USED FOR THE OVER CURRENT EARTH FAULT RELAY CAN USE FOR UNBALANCE ALSO?
depending on what we can choose the rate of mccb considering that we know the total load
How can you test the vector group of power transformers?
Do power transformers have an Automatic Voltage Regulator (AVR) just like the alternator/generator in a power system?
why we did not get shock by touching nuetral of any single phase supply of a electrical equipement?
give me applications of sequence bridges . (used in 3 phase un balanced systems)