Answer / carl_ellis
Answer: 239.2 mmH2O
Present max flow rate = 1700 nm3/hr
Present max DP (at max flow rate) = 120 mm H2O
New max flow rate = 2400 nm3/hr
New max DP (at new max flow rate) = x
2400/1700 = 1.412 or an increase of 141.2% in flow rate.
The DP and the flow rate relationship is a square root relationship, but the calculation is based on normalized percentage.
X = 1.412^2*120
X = 1.993*120
X = 239.2 mmH2O
The increase in max DP from 120 to 239.2 mmH2O is an increase of
239.2/120 = 1.993 or 199.3% increase in max DP at max flow rate.
Sq root of 1.993 = 1.412 or 141.2% increase in max flow rate (2400/1700)
Carl Ellis
Measure First
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / alim
I think the equation is not straight forward, you need some repetition formula for calculating this.
Normally, I will use some software to do this kind of calculation such as InstruCalc. The data that you presented in the question is not enough. I am assuming that you are using the orifice in as the flow element, then you still need viscosity and specific gravity of the fluid.
| Is This Answer Correct ? | 1 Yes | 1 No |
Are Coils of Electromagnetic flowmeter in direct contact with fluid material
how to calculate the temp. of RTD&Thermocouple when we got some mV r Ohms?if anybody has d chart pls mail the chatrs to me...
difference b/w single acting and double acting actuator by using application only?
what is the main supply source for pressure transmitter?
An atmospheric storage tank has a diameter of 20 m and a height of 8m.It is half-full of liquid with the remainder of the space containing air normally at atmospheric pressure. If the connection to atmosphere is accidentally closed off and 10 cubic m of liquid removed, what happens to the internal pressure of the tank? What are the possible consequences for the tank?
What is Predictive Maintenance
given a processor batch of 1000 resistors moving on the conveyor belting in a large factory. the resistors is value at 10k ohms each but when the resistors reach the quality control, some of the resistor has been rejected caused by failure in manufacturing.the high quality measurement is used to determine the failure. describe the instrumentation terminology in measurement of a system above with explaining the important in:- -reliability -sensitivity -repeatability -precision -range -resolution -linearity -hysteresis -error -accuracy (answer must related to the scenario above)
few questions on RS 232,1 question on relationship of impedance and turns ratio, many questions on flowmeters
what's meanning of 1250KVA and how to calculate with Volttage and Current. answer give with example.
In my company plc based winders are operated. one day there was a data transmission failure alarm shown on pc. as per sir instruction we have reset master plc but winders were not triped and alarm gone. so what master plc do?
whatis virtual instrumention?
what pressure transmitter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)