Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


i want the equation of this question.
Tranmitter range is 120 mmwc and dcs flow range is 1700 nm3/hr. if i want to change dcs range from 1700 to 2400 nm3/hr then how much dp i have to enter in transmitter

Answers were Sorted based on User's Feedback



i want the equation of this question. Tranmitter range is 120 mmwc and dcs flow range is 1700 nm3/h..

Answer / carl_ellis

Answer: 239.2 mmH2O

Present max flow rate = 1700 nm3/hr
Present max DP (at max flow rate) = 120 mm H2O

New max flow rate = 2400 nm3/hr
New max DP (at new max flow rate) = x

2400/1700 = 1.412 or an increase of 141.2% in flow rate.

The DP and the flow rate relationship is a square root relationship, but the calculation is based on normalized percentage.

X = 1.412^2*120
X = 1.993*120
X = 239.2 mmH2O

The increase in max DP from 120 to 239.2 mmH2O is an increase of
239.2/120 = 1.993 or 199.3% increase in max DP at max flow rate.

Sq root of 1.993 = 1.412 or 141.2% increase in max flow rate (2400/1700)

Carl Ellis
Measure First

Is This Answer Correct ?    13 Yes 0 No

i want the equation of this question. Tranmitter range is 120 mmwc and dcs flow range is 1700 nm3/h..

Answer / alim

I think the equation is not straight forward, you need some repetition formula for calculating this.

Normally, I will use some software to do this kind of calculation such as InstruCalc. The data that you presented in the question is not enough. I am assuming that you are using the orifice in as the flow element, then you still need viscosity and specific gravity of the fluid.

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

Are Coils of Electromagnetic flowmeter in direct contact with fluid material

4 Answers   TATA,


how to calculate the temp. of RTD&Thermocouple when we got some mV r Ohms?if anybody has d chart pls mail the chatrs to me...

1 Answers  


difference b/w single acting and double acting actuator by using application only?

2 Answers   McDermott,


what is the main supply source for pressure transmitter?

1 Answers  


An atmospheric storage tank has a diameter of 20 m and a height of 8m.It is half-full of liquid with the remainder of the space containing air normally at atmospheric pressure. If the connection to atmosphere is accidentally closed off and 10 cubic m of liquid removed, what happens to the internal pressure of the tank? What are the possible consequences for the tank?

1 Answers  


What is Predictive Maintenance

0 Answers  


given a processor batch of 1000 resistors moving on the conveyor belting in a large factory. the resistors is value at 10k ohms each but when the resistors reach the quality control, some of the resistor has been rejected caused by failure in manufacturing.the high quality measurement is used to determine the failure. describe the instrumentation terminology in measurement of a system above with explaining the important in:- -reliability -sensitivity -repeatability -precision -range -resolution -linearity -hysteresis -error -accuracy (answer must related to the scenario above)

0 Answers  


few questions on RS 232,1 question on relationship of impedance and turns ratio, many questions on flowmeters

0 Answers   Monnet,


what's meanning of 1250KVA and how to calculate with Volttage and Current. answer give with example.

3 Answers  


In my company plc based winders are operated. one day there was a data transmission failure alarm shown on pc. as per sir instruction we have reset master plc but winders were not triped and alarm gone. so what master plc do?

0 Answers  


whatis virtual instrumention?

5 Answers  


what pressure transmitter?

8 Answers   Bhel,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)