In close vessel/ drum why we use d.p. transmitter of -ve
range i.e. (-)500 to 0 mmwc.
Answers were Sorted based on User's Feedback
Answer / venbha123
If the LP leg of the transmitter is kept dry, steam may get condensed in the LP leg because of which the level indication may be wrong. Hence We are using wet leg for LP side of the transmitter, which is initially filled with pure water. When the drum is at zero level, the pressure difference is only the head pressure acting on the LP side - that is 100% level head at LP side. Normally in DP transmitter the HP side pressure will be more than the LP side. In this case since the pressure in the LP side is more than the pressure in HP side the range is mentioned as negative. At 100% level both the head pressures at HP & LP are the same, the DP becomes zero. Therefore the range is mentioned as: from negative value to zero.
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / ayaz
IN CLOSE VESSEL/DRUM
we use wet leg mean(low impulse line fill with same liquid)
we know that our measurement is when right then dp is creat
and when we use without low side filling and hp side only pressure the steam create pressure on lp side so dp not create and show wrong indication
so we use fill lp side pressure and address in negative and when hp side posative or actual pressure create a dp in right indication will show
Is This Answer Correct ? | 0 Yes | 0 No |
what is ILD
What is difference between scada and virtual instrumentation?
What is transducer
how to calibrate mass flow meter (Coriolis)? Example calibration range: 0 to 2500 kg/hr line size 3" fluid: Etheline glycol (MEG)
what is the difference between active and passive loop ?
what is solenoid valve?
I want to know the questions asked in ONGC interview(after being selected in the written exam) for Instrumentation branch.Kindly help.
PT RTD Range: -200 to 500 degree celsius If I configured in DCS Lower range and Upper range . In face plate it shows red colour due to overa range how was the characteristics look If the temperature is more than operating range. how was the characteristics look . whether its in Resistance vs Temperature curve is Linear or Non linear
A temperature sensor (RTD) connected via a temperature transmitter is adjusted to give an output of 4ma at 60 deg and 20 ma at 600 deg. This output (4-20ma) from the transmitter is connected to an IGBT-inverter to control a high speed (-12,000 to +12,000 RPM) DC motor. And in the inverter it is programmed as, for 4ma the motor speed will be -3,000 RPM and for 20ma the motor speed will be +10,000 RPM. The question is : If the motor speed is +5,500 (RPM), what will be the temperature? (-sign indicates that the motion is in reverse direction).
what is beta ratio?
I want to take temp. data from recorder to computer. Which communication system is best from this option(Rs 232- 485/ethernet/USB)?
Single acting ON-OFF valve. it is air to open. when sov energized , valve will be open, so during that if air fail then what will be the condition of valve ( open or close ) ???