Capacitor panel CT is normally fixed on Y phase of the main
panel.why???
Answers were Sorted based on User's Feedback
no my friend,it depends on APFC relay,
1.in L&T make APFC relay ct is looped in R-phase.
2.in Sentron make APFC relay ct is looped in Y-phase.
3.in Sycon make APFC relay ct is looped in B-phase.
if you have any dout see all above relays wiring diagram.
For measuring PF APFC relay required any two phases & one CT sence on remaining phase from main PCC Phase.
Eg.(R-Y phase & BCT from Main Panel)
From--Rajendra Sawant
Miraj.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / zia
Good day friends
some time some of factory's lode not same in R,Y,B.
Example R=155amp, y=140amp, b=145amp which one we selected
for apfc relay for sense observing p-f . we are selected the
maximum amp flow phase.it can be R or Y or B. for good pf
rating.
so its a CT depends on the flowing amp of the phase
Is This Answer Correct ? | 3 Yes | 1 No |
Thanks Zia Mam,For Sharing Additional information,but what about the manufacturing relay companys who manufacture the relay which has R,Y,B phase Selection of CT which i have mentioned in above answer,should we select our relay as per our Phase Load.
From-Rajendra Sawant
Is This Answer Correct ? | 0 Yes | 1 No |
why no load characteristics of generator also called as occ
why we measure ouput of transformers in kva.
Why does The speed of motor used in elevator remain constant irrespective of load??
What is the purpose of Vector Group in transformer?
1 Answers Andritz, ThyssenKrupp,
In the Variable Voltage Variable Frequency Drive, how the Voltage and Frequency varied ? Is it varied in the Inverter part of the Drive ? Please give us supporting document if any.
What is rccb?
In 11kv transmission line whats the maximum power can be drawn?
What is Automatic interlocking circuit dighram between two contactor for DG SET panel.
generaly all power generating devices is expressed in KVA or MVA then why power ststion is expressed in MW
What is sequence network? Discuss all three types of sequence network.
What can be a rating of a transformer(KVA) if the load is about 1000KW?illustrate by showing formula?
Sir, I need a power supply at 380V. The supply I get in three phase is rated 415V. The total supply I have from the supply company is 70KW. Kindly inform if it is better to use a voltage stabiliser for this purpose or a transformer