WHAT IS THE DIFFERENCE BETWEEN UNDERVOLTAGE COIL, CLOSING COIL
AND SHUNT TRIP COIL OF AN ACB?
Answers were Sorted based on User's Feedback
Answer / karna
Under voltage coil means it will energized when supply
available, closing coil means it will operate when we are
giving closing command at that time it will operate , shunt
trip means it will operate when we are giving trip command
manually or through fault. CLOSING COIL OPERATE MEANS WE
WILL GET OUTPUT SUPPLY FROM THE ACB TERMINALS , SHUNT TRIP
COIL OPERATE MEANS IT WILL DISCONNECT THE OUTPUT SUPPLY OF
THE ACB TERMINALS. IF UV COIL USED IN ACB MEANS WITHOUT
INCOMING SUPPLY WE CAN'T CLOSE THE ACB.
Is This Answer Correct ? | 59 Yes | 4 No |
Answer / nirmalraj
cc used for closing the breaker contact, tc used for trip/open
the breaker contact and uv coil used for spring charge
interlock. if no supply manual spring charge is possible,
supply is present manual spring charge is not possible
Is This Answer Correct ? | 12 Yes | 8 No |
draw a dol with the following rtds,stop/start,ct,vt and o/l supply is 6.6kv and the coil is 110v
Petroleum jelly is applied to the terminals of the lead acid battery is to prevent?
in 132 kv transformer , in which range of transformer oil bdv required ? if it has around 50-55 , then how it was insulated the winding ?
why our indian system choose the 230 volt for single phase&415 for 3-phase voltage,in forign side 110 volt is used what is the difference
A 6-pole, 50 Hz, 3-phase synchronous motor and on 8-pole, 50 Hz, 3-phase slip-ring induction motor are mechanically coupled and operate on the same 3-phase, 50 Hz supply. If they are left open-circuited, then the frequency of the voltage produced across any two slip rings would be
how calculation to be done of cable size/o.h. conductor size of 11kv h.t.for the load of 2175 kw
while conducting an experiment why we connect the armature rheostat in maximum position and field rheostat in minimum position
What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works?
in VFD when freq is reduce the voltage will reduceor not if it will reduced upto ...
When we synchronize the Generator BKR with TIE BKR then Gen BKR is hold but TIE BKR is Tripped on Non directional over current but when TIE BKR is Syn. with Gen. BKR then no fault occur so what is the problem
what is S.T?specify the range?
Will an earth leakage trip be activated if the component or wiring is faulty on low voltage equipment.Example An electrical Cat Scarer placed in the garden and water gets into the wiring.