in GEAFOL Cast-Resin trnaformer of 11/.72kv which has
tapping of 11550v,11250,11000,10246v in primary side. To
obtain 700v. which tapping should be used of HV side as we
have 11000v/720v tapping now .
If the primary voltage [supplied by Utility] it is NOW 11
kV and your transformer at no-load shows 720 V at its
secondary terminals the ratio primary/secondary voltage is
11/0.72=15.278. If you want to reduce the secondary to 700
V you have to change the ratio to 11/0.7=15.714.
Let's say the rated secondary voltage [at no-load] is 720 V.
That means the ratio 11250/720=15.625 it is the most
suitable and you'll get 11000/15.625=704 V at secondary
terminal [at no-load].
Is This Answer Correct ? | 1 Yes | 0 No |
-What shall be short circuit current of LV switchgear for a 1000 kva, 11.415kv, 3 phase tranformer with 5% reactance.
how to calculate percentage impedence at 75 deg C at normal tap
What is maximum power transfer theorem?
What is boucholz relay and the significance of it in to the trformer?
when we are going to higher voltage level in substations why we are using Sf6 circuit breakers instead of Vacuum circuit breakers.
WHAT IS LINIER MOTOR?
What is accuracy of a measurement?
why we remove capacitor connection in 3 ph Induction Motor while taking noload test.
what happen if i connect DYn11 and DYn1 vector group transformer in parrallel?other things are same like votage ration,x/r ratiob etc...
What is the use of arc chute in ACB?
how electronic energy meter works?
HOW MUCH CURRENT CAN A 3 -1/2 CORE 100 MM WIRE CARRY