how much current capacity 250 amp. mccb please tell me about
whats are the reasons to trip 2 or 3 times in a night. and
what are the steps to short out this problem
Answer / k.k dash
kindly see the breaking capacity of 250 amp mccb,if it trips more than two times kindly replace the mccb with new breaking capacity such as 25 ka, 35 ka,or 50 ka,so that it capable for taking the current
Is This Answer Correct ? | 4 Yes | 0 No |
Whay you want to change your job.
why we use single core 630mm2 cable for transformer secondary side
Which ciass CT can be use in diff. protection. Can be use 5p20?
What is the difference between resistance grounding system and resistance earthing system?
what is suroounding current of dg set?
What is reactive power and where it is used.
DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED R VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV
why capacitor do not switch ON the DG power? (I had checked, capacitor ON in DG power that time current rating was reduced.)
what is hysteresis loss?
Explain Clearly Pahase and Neutral?
What will happen if we introduce negative feedback to a control system that uses a positive feedback?
What is the lower limit of megger value for 66/11KV power Transformer ?