what are the documentation and instrument identification system used to identify the correct device to be calibrated? name atleast three.
Answer / carl_ellis
- P&ID: tag name/number for the instrument in question,
but not the location
- Loop diagram shows tag name/number, has a location
description (field, panel, I/O rack, control room) and
wiring terminals ID (are wires 1578 and 1579 connected to
the instrument in question?)
- ISA's instrument spec sheet has a section for calibration
with input/output, but more importantly, the following
section has Component Identification by manufacturer and
model number. The serial number isn't there because this
document defines the functionality, not a specific device.
- The company's "Instrument Specification Data Form" should
have a field for a location and instrument serial number
- Calibration data sheet should have a field
for "Location", tag and serial number.
- There should be a stainless tag on a field instrument
- The handheld communicator displays the tag name when
connected. The instrument's tag name should match the work
order's tag.
- The local "Calibration status label" on or inside the
instrument always has a tag ID.
Carl Ellis
Measure First
Is This Answer Correct ? | 7 Yes | 0 No |
Im working in a shopping center, it is also hotel and office building, two towers exactly and someone is proposing a PLC control for the HVAC system, but Im thinking of a DDC control system. in this case what is the difference between PLC and DDC control?
How to convertion 100 m3/hr to mmH2O or to Kg/cm2?
How does a single acting, spring return ball valve actually work? Does it require continuous air supply?
0 Answers Process Control Technologies,
in a electronic controller why we are using 250 ohm resistance in input signal?is i/p is necessary in control valve when we are using electronic controller give details?
What is Cu-100 and Cu-1000 ? and tell me its application ?
why we use 0.2 to 1.0 kg/cm2 output in control valve
When doing a liquid seal on a differential flow transmitter , most of the time the sealing liquid will be heavier then the process fluid. For wich application will the sealing liquid be lighter than the process fluid if transmitter is mounted below the process line.
What is the meaning of slope in PH transmeter?
How we calculate orifice plat size???
where are following valves are applicable to install. can any valve be installed any line. globe valve butterfly valve boll valve gate valve
what is PID n give me brief info. about P&I&D.
My friend has faced this question! I don't know clearly. So please anyone give me the correct and short answer to this question? What is variable frequency drive? Types, what is star to delta? Why this arrangement necessary?