why temperature transmitter is showing ambienttemp.but 21.5ma.
alarm AO showing at the display &how to sloves this problem.

Answers were Sorted based on User's Feedback



why temperature transmitter is showing ambienttemp.but 21.5ma. alarm AO showing at the display &..

Answer / carl_ellis

When you need troubleshooting assistance you need to supply
certain critical information:

1) Has the device ever worked correctly before for some
time period and then failed?

Or is this a first time commissioning issue?

2) What is the brand name and model number of the device?

3) Because all devices have an input and an output, exactly
what each is (is your sensor one thermocouple, two
thermocouples, or one RTD?)
- You do tell us the output is 21.5mA.

4) What are the error codes or what the error symptoms?
- You mention the display shows ambient temperature

5) What you've done to troubleshoot the problem, like
substitute a known source (simulator) and the result
was . . . . ?

Evaluation:
ambient temperature: A short circuit (a wire) across the
terminal inputs of a thermocouple input will display near-
to-ambient temperature, specifically the temperature of the
terminal block connectors. The value is the cold junction
compensation (CJC) temperature.

Some high end transmitters will show the CJC temperature.
Is the display stuck on the CJC temperature, rather than
its input? Is there a short across the (+) and (-) input
terminals?

21.5mA is a very common fail-safe alarm level, outside the
normal 4-20mA range, but indicating that there is a serious
fault in the transmitter setup or operation. If the fail-
safe is configured for fail high, an open input (among many
other things) could cause the fault.

Smart transmitters generate an error code and save it. If
the transmitter has HART, the error code is in one of the
diagnostics registers, but a HART communicator is needed to
access the error code.

Carl Ellis
Measure First

Is This Answer Correct ?    2 Yes 0 No

why temperature transmitter is showing ambienttemp.but 21.5ma. alarm AO showing at the display &..

Answer / carl_ellis

A short circuit (both thermocouple wires touching each
other) in the thermocouple extension wire leads will create
an ambient or near-ambient temperature reading, but I am
unaware of any temp transmitter that can detect that problem
and go to fault mode at 21.5mA.

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

What is linearity of RTD over 0 to 200 degC?

1 Answers   Honeywell,


what is effect of specific gravity in differential level transmitter , explain formula related with this .

0 Answers   Flour Tech Engineers (P) Ltd,


Define all the process Variable and state their unit of measurement. ?

0 Answers  


how to turbine speed measurement?

0 Answers   Jindal Steel and Power,


why 4 to 20 ma? why cant some other range?

3 Answers  






What is frequency factor in massflow meter? When using frequency output?

0 Answers   PCMIL,


What is compensation for flow ? Why we use compensation ? What are the factors of different compensation ? We not use then what problems may happen ?

0 Answers  


can we use flow transmitter instead of level transmitter?

7 Answers  


if we have 450 mm heigth boiler drum level ,so what is span & zero value for a dpt tranmitter

4 Answers  


plz exlain the dcs system of ABB sympony hamnony

1 Answers  


how to calculate flow by dp transmitter?

4 Answers  


Hi at present i m wrking with tire industry as a manager having gud ctc. Nw I am selected for 1 of the best chemical industry but my ctc is lower than current n also i hv 2 compromize vit post as post is also lower. I hv 6 yrs of exp in various type of industry. Should i join chemical industry as there ar lot of gud instrument than tire? Financialy i can manage 4 more 2 yrs. Bt during wrking vit tire industry i found there is very less instrument n feel that opportunity is less. Pl ans quickly. I have less time to decide.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)