If we increase D what will be the controller action?
Answers were Sorted based on User's Feedback
Answer / sks
well, increasing D action for a controller can make a
controller random in error elimination because even for a
step change D generates a spike( means tries to compensate
for change very quickly). if its increased to its limits, D
action will overtake the process value change and this will
cause further offsets that I action wouldn't be able to
compensate due to its slow response against such a rapid error.
result is a quick overvalued offset !
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / david
In PID
P is Propositional means it will adjust the output propositional to the error. For example a Tacho connected to a motor, to control it's Torque and RPM at a constant level.
I is Integral means calculating the area, according to the area of the error the output is adjusted. For example, the difference between positive cycle area and negative cycle area.
D is differentiation means calculating the angle difference and driving output for example
In a 3-phase system, If the load on R-phase is more than other two phases, phase angle
difference will occur so it will calculate the angle and drive output For example Auto Power factor adjuster.
Is This Answer Correct ? | 0 Yes | 0 No |
what is the differnce between PLC & DCS
why is not useing in boiler skin thermocople
Explain the thermocouple and RTD?
How to derive IO Count (AI, AO, DI and DO ) from a Field instrument (FI) Bill of Quantities (BOQ) given by client.
what is difference between 1/2"NPT & M20 x 1.5 cable gland?
a flow transmitter [range-0-400mbar] connected in process line. please explain me how to calibrate the flow transmitter , & how to do static error
Please can anybody tell me the step by step procedure for calibrating the Pr,Lvl,Fl,Temp transmitter on process?
How to check the SCAN time of DCS ,n dont give therotical answers .How to check the SCAN time of DCS during FAT?
pl give the guidance for DUBAL written test
Can we place a Control Panel in Hazardous area Group IIC ? If 'yes' then is there any approval required? If 'yes' then there is any specific IP rating or any standard required? If 'Yes' What is MOC of control panel?
hi everybody. right now i am working with thermal power plant. our company plant is tripped because of program corrupt. i would like to know is it possible when the plant is running. we are using FREELANCE ABB800F CONTROLLER.
Please any one can explain how to calibrate transmitter (smart) online with out remove from the container suppose it is interface level or static pressure level measurement we dont want to remove transmitter from the container mean it is running plant please give me detail. thankx brothers