what will happen if we double the input frequency of a
transformer keeping the voltage constant?
Answers were Sorted based on User's Feedback
Answer / santhosh
hysterisis losses and eddy current losses depends upon v/f
ratio hysteris loss=kB^1.6 f v if v/f ratio is constant
hysterisis loss is prportional to frequency i.e B is
constant if v/f is not constant hyloss is prop to f^-0.6 so
if freq is is increased hyloss is reduced but eddy current
loss remain constant because eddyis prop to B^2 f^2 so if we
sub v/f in the place of B eddy loss is prop to V^2 so it is
indepentent of frequency
Is This Answer Correct ? | 38 Yes | 1 No |
If the frequency applied to a transformer is increased, the
inductive reactance of the windings is increased, causing a
greater ac voltage drop across the windings and a lesser
voltage drop across the load. However, an increase in the
frequency applied to a transformer should not damage .
But, the applied frequency of the transformer is less than
the normal Frequency, the reactance of the windings is
decreased and the current through the transformer winding is
increased. If the decreasing frequency is enough, the
resulting increasing current will damage the transformer.
For this reason a transformer may be used at frequencies
above its normal operating frequency, but not below that
frequency.
Is This Answer Correct ? | 18 Yes | 4 No |
Answer / dinesh b.e
The same current will flow for both 50 and 100Hz frequency.The Only difference is hysteresis losses will be more if 100Hz given as input. .Which only used to test the transformer's for 60second to check insulation withstand capability. .Generally hysteresis losses will be there in transformers which depends upon core quality. .Magnetising and Demagnetizing of core for 100cycles leads to increase in hysteresis loss.That is losses in form of heat .Which gives raise to increase the oil temperature.Due to this effect , chemical reaction Will take place between copper and sulfur content in oil.finally formation of copper sulphate,which acts as a conductor and settled upon windings . circulating current Will be there due to mmf.which leads to heat and damages the windings dielectric strength.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shinde kv
when we applied double freq. that time eddy current losses
increase means iron losses will be increase hence increase
the heat loss.
Is This Answer Correct ? | 8 Yes | 14 No |
Answer / daxity
Current is the RATE of flow of CHARGE in a circuit.
Frequency is the number of CYCLES per second......NOW..if
frequency is increased,the rate of flow of charge is
increased that is current,which may damage the insullation
on transformer winding due to over heating.
Is This Answer Correct ? | 1 Yes | 8 No |
we have total 1000hp motors we paid 7 laks rupees how to reduce power bill
WHAT IS THE REASON FOR LOW VOLTAGE IN HOUSES?*
in transmission line 11kv is step up or step down? why?
in basic 2 phase will short means tripping the power but spot welding 2 phase shorting but not tripping it will welded why.....(Q)
When VFD is connected to a 3 phase main supply there is load current difference between incomer to VFD and outgoing from VFD.
Is there any problem about which the drive (inverter) doesn't show/display the alarm and/or fault but instead of this , it doesn't work ? I want to know that could there be any kind of problem in the drive when the drive doesn't display the alarm and/or fault ?
what is calculation mathod/formaulla for deciding Size of busbar (Copper/ aluminum)for L.T. panel on Various Fault level like 50kA,25kA,10kA
How to convert KV into MV in a Transformer?. dont say multification of 1000.pls give practical convertion factor.
Why cpaciter opposes sudden changes in voltage?and how?
when we use neutral line as grounding.
What is diference between ELCB & ELMCB?Also how its application for use in design area?