how to calculate the cable size for 500 kva transformer?
Answers were Sorted based on User's Feedback
Answer / ezhil
the full load amps of 500kva transformer is
kvax1000 / 1.732 x v
500x1000 / 1.732x415
500000/719 = 695A
Hence we can select 2R X 3C X 300SQMM
Is This Answer Correct ? | 15 Yes | 3 No |
Answer / satyendra kumar
find the total load whatever rating of trnsformer---------------i=kvax1000/secondary voltage. we find total load then select of cable size i think 500sq2mm
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / dharmendra
post your full question input cable or output cable
you can use V1xI1=V2XI2
Is This Answer Correct ? | 6 Yes | 11 No |
why commutator are not used in rectification purpose in power electronics?
1)Explain why the cradle guard is used on railway crossing in overhead line construction?
Application Comparison between 22KV (UE)and 33KV (E) system. Are we allowed to use 33KV (E) cable in lieu of 22KV (UE) cable. What are the technical disadvantages.
Describe the method of Plate Earthing.
how to wiring it with contactor and timer together
working of a diesel generator.
34 Answers ABC, AC, Cognizant, CTS, Directorate of Lighthouses and Lightships, KSL, Quippo, Shree Renuka Sugars, SRF, Svam Power, Tech Mahindra,
How can we design a HVAC Plant room which includes AHU,FCU,Chillers,Cooling towers, Pumps etc & how will they work? any Drawing if possible?
WHY RATING OF VCB NOT LESS THAN 630A
what is relay type VDG,CDG,VTT ect?
What are the Full Forms of TVM, MTL, CVT ?
12.5 tons a/c is their how much kva generator can recommend to the customer.
I have a situation to design sub-Distribution board/Panel meant for feeding power sockets. In the incomer CAN i Take TP MCCB with Neutral Link and All the outgoing feeders with to sockets with TP MCCB and Neutral Link? P.S : My System is IT Earthing