What is the function of Antipumping Relay and Lockout Relay?
Answer / avdhesh
Antipumping Relay : It is generaly used in series of
closing coil of breaker. The function is to cut off the
supply of closing coil immediately after closing of
breaker. This is required as coil is not designed for
continous rating.
Lockout relay : This is also used in closing ckt of
breaker. This is basicaly latched relay which inihibit the
closing of breaker for defined time if relay is operated.
Lockout relay can be self reset or manual reset (choice)
after definite time.
| Is This Answer Correct ? | 1 Yes | 0 No |
how to find the transformer effiiency
What do you mean by the zone of protection?
What is VCB'S @ ACB'S.Plz explain Briefly
why most of junction box vendors providing T5/T6 Temp class jb's for T3 area any special reason?
how can I improve the current at same voltage? if yes is there any circuits?
What is the different between buchholz relay and pressure relief device?
why we are using2 wave trap in a feeder?
How can we calculate D.C.Load current in terms of A.C. load current?
Why transformer is rated in kva?
Why we call cable rating in SQ.mm.If it is 240 SQ.mm how much the diameter possible?is there any calculation ?
I want to know the standards for earthing system as per IEC, BIS & IEEE.
What is the basic difference between 90% stator earth fault and 100% stator earth fault, and its phenmenona?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)