Why is it that polarization index type test is required for
MV and HV motors and not for LV motors?
Answers were Sorted based on User's Feedback
The polarisation index is used to check the insulation of
MV and HV motors because it is more accurate. Also it
allows a lower voltage than the working voltage of the
motor to be used. In LV motors the megger test is usually
twice the working voltage. If this was used on an 11kv
motor the megger would need to be 22kv.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / cr
As we r letting high current pass through the winding using ht megger,there by improving I.R because the heat produced and the ir ratio for 10 to 1 minute should be around 2.otherwise the insulation can be said to be contaminated with foreign meterial , this check is priority for ht motors
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / prashant
because the moror windig is balance or not and winding of the motor is open or not
| Is This Answer Correct ? | 0 Yes | 7 No |
how to calculate current carrying capacity in power cable?
what are the safety in transformer,diesel generator,ups, chiller plant,h.t. , L.t. , sewage treatment plant(stp),water treatment plant(wtp), fire. plz ans. me in detail if you know any of the mention above. i urgently need
2 Answers Claris Lifesciences, EFS,
How to Select transformer for 100HP motor plz... With calculation
what is the difference between 3 phase 3wire &3phase 4 wire meter?what is the advantage of 3p3w over 3p4w?
I've heard that most of the substations are rated in multiples of 1.11 because of form factor.What is form factor?
What are the functions of different probes used in cro?
We have one 500KVA transformer. We have tested REF relay and commissioned. After one and half year, due to some ground fault in one of the DB circuit Transformer tripped by REF relay. What will be cause and remedy. Please advise?
MY QUATION IS ABT THE MAIN POWER TRANSFORMER IN STEEL PLANT , I WISH TO KNOW THAT WHY TRANSFORMER PROTECTION NOT TRIP AS CABLES ON THE SECONDAY SIDE IS WATER COOLED. TRANFORMER DETAIL NORMAL KVA--150 KVA PRIMARY VOLTAGE --34.5 KV SEC.NO-LOAD VOLTAGE---1.290-908-690V ( WITH PRIMARY DELTA CONNECTED) CONNECTION--D/d (EXTERNAL CLOSED) CONSTANT RATEING FROM--1.290-908V CONSTANT CURRENT FROM--908-690 VECTOR GROUP--D III
why 30 ma elcb is used ?why cant 100 ma?
If not maintained 3 phase clearance,what happened ?
What is evaporator & condencer & compressor
WHICH SIZE A.B.CABLE IS USED FOR 11KV.
0 Answers Novel Tech Park, Power Grid,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)