Answer / vikas thokale
as LT panels are designed for 240 or 440 volts and HT panels
are for 11kv and more.And to deliver same power this high
voltage requires less current.
as
power = voltage x current
that is why HT panel cable size is less than LT panel cable
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / sheikh
Because High Voltage (ht) drawn low current therefore there is
not neccessary to use large size of cable. Lt side drawn more
current so there is neccessary to choose large size of cables.
Is This Answer Correct ? | 7 Yes | 1 No |
because HT Voltage having a high voltage & low current and we are providing high insulation in bitwen of phases.LT voltage is having low current & high current. we are providing low insulation in bitwen of phases.current depending of cross section of cable.More cross section more electrons flow & less cross section less electrons flow.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / hemalatha
because HT Voltage having a high voltage & low current and
we are providing high insulation in bitwen of phases.LT
voltage is having low voltage & high current. we are
providing low insulation in bitwen of phases.current
depending of cross section of cable.More cross section more
electrons flow & less cross section less electrons flow.
Is This Answer Correct ? | 0 Yes | 0 No |
What is the basic difference between AVR and stabilizer?
2 Answers Gujarat Alkalies and Chemicals GACL,
Why ELCB trip, when neutral touch with ground?
what will be the effect on the voltage .if power frequency is increasing or decreasing.
I have running 4 generator in paralel.All generators Voltages is same(470 V),KW also same (100 KW) but only No2 generator Amper is high than another generators. DG No:1,3,4 470V,100KW, 150 A DG No:2 470V,100KW,400 A
How much heat will a 2500 KVA transformer will generate ?
When we use air circuit breaker, it has O/L protection ,time delay SC protection, Instataneous SC protection & ground fault protection. They all have some setting range. But what is the suitable/allowable setting for the above protection which will be safe for the equipment? For example-O/L protection setting have a range of (0.4,0.45,0.5,0.55,0.6,0.65,0.7,0.8,0.9,1.0)xIn Time delay SC protection have a range of (1.25,1.5,2,3,4,6,8,10,12)xIn Time delay setting is 0.02,0.1,0.2,0.3,0.4 Instataneous setting is fixed to 20xIn Gound fault setting is given 100A,300A,600A,900A,1200A This setting are for 2500A ACB. So what will be the basic allowable setting for the above protection? is there any formulae to calculate this<
Why mostly conductor made by 7 nos wire?
What is domestic transformer? Draw the connection of domestic transformer.
What is the function of the serge absorber?
is there any lightning by passer is arranged in ship like buildings?
The importance of resonant filters in converters?
why humming sound occured in HT transmission lines.