How to select cable rating for HT/LT Panels
Answer / sudhakar g
If we take the LT panel incoming of the breaker is 1600A
and the transformer rating is 2000KVA.
We have to select the cable for that t/f to incoming
breaker in LT panel
400Sqmm AL cable carry 315A (POLYCAB) then we go for 6Runs
from T/f to LT panels
It is simple to cable runs of the T/F to I/c of the panel
Is This Answer Correct ? | 6 Yes | 4 No |
i want the formula of total eletical knowledgement
if suplly 11kva its give 440volts then if suplly is given 10kva whats the volts given
why we are used armed coble for wiring of 3phase motor?
what is the meaning of TPN
why only 11kv level is used for transmission purpose? why not 230v?
At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC 54A as per the nameplate. At the time of starting it draws 840A instead of 390A (7.2%). As per the data sheet also its 390A starting current. it thru a dol starter from the MCC. can anyone tell what is the problem in the motor
What is the meaning of Fault level rating?
1 Answers Balrampur Chini Mill,
how much maximum load a 2 core (Single phase) 16mm aluminium wire can take ?
how braking & making capacity of circuit breaker is calculated?
We have 11kV/110V three phase indoor potential transformer in 66/11kV Sub-station, where the failure of PT is frequently happening and the rating of the PT is 0.2 class accuracy, with primary star and seconday (two cores) star connected. Some experts has suggested to not to connect the PT Primary neutral to the ground because when transformer neutal NCT connection is loose; the faulty current will flow through the PT primary neutral, resulting into failure of PT. My question is: Is it necessary to remove the primary neutral connection of the PT from ground? if not, what would be the reason for failure of PT. Please guide me.
Dear All we are having a problem in G120 BOP showing alarm A0503, F0052, F0060 we can not remove fault alarm ,Please any body help us. kowsar
what is the minimum recommended leakage current of an earthed cable connected to the body or skid of an alternator