Why the transformers are rated in KVA ? in new view
Answers were Sorted based on User's Feedback
Answer / pradyumna chandra panda
By help of power trangle pf= value of cos thita (cos fi)=
b/h=active power/apparent power. Active power (kw)is the
real or true power which the transformer give for a
aparticular load (useed power)and Apparent power(kva)is the
supply power for that particular load. That a 100 kva
transformer can supply/give 100 kw resistive load and
incase inductive circuit a 100 kva rtransformer give 80 kw
inductive loadat at.8 pf,and 75 kw inductive load at.75 pf
etc but the pf of the load is not known before that which
types load (resistive,inductive or capacitive)to be
connected across the suplly, this is only why the
transformers and Alternaters are rated in kva and it is
meaningless discuss about iron loss & copper loss because
the UPS and inventers are also rated in kva.
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / praphulla bansal
KVA is mentioned to take care of PF issues of the load. At the same time, rating of transformer is given a limiting PF. This means a 100 KVA transformer and limit of 0.8 PF will limit load to 80 KW irrespective of load PF as unity.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / md. abdullah al mamun
I think Copper loss of a transformer is related to current
and core losses are related to voltage so that VA should be
the rating of a transformer. But in a large transformer it
is rated it KVA. Also KVA rating Indicate the Maximum
Current Rating of a transformer with a rated voltage.
Is This Answer Correct ? | 0 Yes | 4 No |
What is meant by Guard relay ?
FEINGING DECREASES THE FLUX DENSITY IN THE AIR GAP. HOW?
why dc series motors never start without some load, and what will happen if starting with out load..
WHAT is the no of starts/hr for 3.3 KV, 300 KW motor. Motor is vertical flange type.
What is a liquid resistance starter?where it is used??
If we have 15000kw connected load in a factory than how much power demand sanction should be taken from electricity board. Pls provide complete calculation.
what is the function of a circuit breaker ?how does the circuit breaker function during normal operation of an electrical system
When VFD is connected to a 3 phase main supply there is load current difference between incomer to VFD and outgoing from VFD.
In the solution of load flow eqation, Newton raphson method is superior to the gauss siedal method because (a)the time taken to perform one iteration in the NR method is less when compared to GS method (b)the number of iterations required in the NR method is more compared to that in the GS method (c)the number of iterations required is dependant on the size of the system in the NR method (d)convergence characteristics of the NR mehod are not affected by the selection of the slack bus
11Kv Dog conductor 6/0.186 formula Line Losses ? Length 4.85Km amper ..? 52 Pole Max Load 3200Kw
what is direct dischage of power transformer
What is the range of the stator resistance of 3 phase induction motor?