how i meggar value of 11kv alternator winding.and with meggar.
Answer / kj
See extract from service manual for HV alternator.
A 5000V motorised megger or similar instrument should be
used. Separate the three neutral leads,
ground V and W leads and megger U to ground. Repeat for V
phase with U and W grounded and W
phase with U and V grounded. Minimum acceptable limits
after 1 minute for each phase are:
New machine 300 M
In-service machine 150 M
The insulation resistance should not be less than specified
and the polarisation index should be in the
order of 2 or greater at 20 ÂșC.
(PI = IR10min / IR1min)
Is This Answer Correct ? | 0 Yes | 0 No |