why slipring motor , at full speed run as squirrel cage motor?
The slip ring or wound rotor motor is an induction machine
where the rotor comprises a set of coils that are terminated
in slip rings to which external impedances can be connected.
The stator is the same as is used with a standard squirrel
cage motor.
The slip ring motor is used primarily to start a high
inertia load or a load that requires a very high starting
torque across the full speed range. By correctly selecting
the resistors used in the secondary resistance or slip ring
starter, the motor is able to produce maximum torque at a
relatively low current from zero speed to full speed. A
secondary use of the slip ring motor, is to provide a means
of speed control. Because the torque curve of the motor is
effectivley modified by the resistance connected to the
rotor circuit, the speed of the motor can be altered.
Increasing the value of resistance on the rotor circuit will
move the speed of maximum torque down. If the resistance
connected to the rotor is increased beyond the point where
the maximum torque occurs at zero speed, the torque will be
further reduced.
NOTE:
The all above said characteristic of slip ring motor is due
to slip ring as well as due to external resistance. All
characteristic are related to is starting period or for
speed control. when we disconnected the resistance from the
circuit then slip ring motor and induction motor will be
same. So, hope the reason, "why slipring motor , at full
speed run as squirrel cage motor" will be cleared.
Is This Answer Correct ? | 2 Yes | 0 No |
WHAT IS THE USE OF EARTH SWITCHES?
What is the suitable rating of MCB used for 1.5 Ton A.C & why?
what is the maximum genarating voltage in india?
Is it necessary to seperate the DG earth grid with Electricity Board earth grid for protecting the DG set. if yes why?
in magnetic field we send current to generate flux,why not voltage?
Can anybody tell the formula to calculate temparature rise in the cable with respect to current?
We have 250 KW x 2 motors, which are load from 25% to 100% varying load in every minute , so how can we compansate the power factor. pl give your opinions on the above subject.
What are the limitations of Kirchoff's laws?
where HT & LT capacitor uses ?
and gate circuit diagram,amplifier circuit diagram
Why electrical heaters are not provided with overload relays in circuits
can we charge 3 ph power transformer delta-star wound with neutral grounded 6.6kV/415V from secondary side(415V) but with primary(6.6kV) open by dg,what are the disadvantages or losses.