how to test a motor from megger
Answers were Sorted based on User's Feedback
Answer / r.kumar
for megger test in motor.......we apply 500v DC supply at terminals and check:
1.phase 2 phase(ohms)
2.phase 2 body (>100MEGA OHMS OR GIGA OHMS)
3.phase 2 neutral(>1 GIGA OHMS)
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bameshwar
To identify the motor winding is correct or not. Body to coil and coil to coil for identify the motors coils shorted or not. It's values are body to coil-infinity or more than 5megaohms,coil to coil - 0megaohms,and coil to othercoil-we are seeing the insulation between coils
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bameshwar
To check the winding s of motor is correct or not (motor shorted or ready to run) it's values are body to coil-infinity, and the coil to coil - 0megaohms, & coil to other coil we are seeing insulation between coil to other coil which is according to motor.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / avvsnmoorthy
motor winding meggar value from bofy t0 phase more tham 5
mega ohm &winding to winding 0 with using 500 volts megger
Is This Answer Correct ? | 2 Yes | 4 No |
why is control bus bi-directional?
bit confused - am i correct in thinking that to determine line to line voltage in a star config 110v 3 phase 4 wire distribution system i would use a voltmeter? I have a circuit configured as an unbalanced load, consisting of three incandescent lamps (1x40w, 1x60w, 1x100w - all 110v rated)connected in a star configuration to a 110v 3 phase 4 wire distribution system. I want to find out what types of meters i would use to obtain: a) each line to line voltage b) the line to neutral voltage across each load c) current flowing in each line and load d) current flowing in the neutral conductor e) power supplied to the loads im assuming i would be using ammeters in series along each line and voltmeters in parallel across each line to neutral? Also how could i predict these meter readings before taking them and with which formulae? Any help would be greatly appreciated A.
what is allowable ac mixing in dc
how wecalculate breaking capcity of acb mcb mccb .explain with example
What are the protective devices in a DC/AC motor starter?
Showing results for capital, machinery, stock,wages, carriage in words, salaries, factory rent, repairs, fuel and power, buildings, debtors, sales, purchases, creditors, return outwords, return inwords, drawings, discount allowed, discount receivable, office expenses, bills payable, bills receivable, cash in hand, cash at bank, office rent comes under debit or credit
what is the diference between the 4pole & 6pole DC Motors & what is advantage 6pole over the 4pole ?
Usually in the L & T make MCC feeders' power circuit,we have BMR after the MAIN CONTACTOR.,can we interchange their position, keeping the control logic same???
if v r considering a 4000/1A ct,if v inject 1 amps in secondary core wat happens?(consider as 2 core ct,each for metering and protection)
What is a commutator?
What is the function of the generator exciter?
which cable is used for 15 Hp monoblock pump 3phase and service wire Distance is 210 feet please tell me cable size Armaured