Answer / r.kumar
for megger test in motor.......we apply 500v DC supply at terminals and check:
1.phase 2 phase(ohms)
2.phase 2 body (>100MEGA OHMS OR GIGA OHMS)
3.phase 2 neutral(>1 GIGA OHMS)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bameshwar
To identify the motor winding is correct or not. Body to coil and coil to coil for identify the motors coils shorted or not. It's values are body to coil-infinity or more than 5megaohms,coil to coil - 0megaohms,and coil to othercoil-we are seeing the insulation between coils
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bameshwar
To check the winding s of motor is correct or not (motor shorted or ready to run) it's values are body to coil-infinity, and the coil to coil - 0megaohms, & coil to other coil we are seeing insulation between coil to other coil which is according to motor.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / avvsnmoorthy
motor winding meggar value from bofy t0 phase more tham 5
mega ohm &winding to winding 0 with using 500 volts megger
| Is This Answer Correct ? | 2 Yes | 4 No |
tell me about your project
From, which load current range ( upper - lower limit current)can Air circuit breaker used for in electrical circuit.
Can RCD's used to protect the VVVF drive if not why.
What is the full form of AND,OR and other logic gates
What are the conditions to be satisfied before connecting two DC generators in parallel?
why capacitor using the induction motor?
How to calculate the current of Highpressure Mercury Vapour Lamp?what is the basis?whether we have to consider power factor or not?
Why AC current leads voltage in capacitor and how?
What is GD2(kg-m2) for Sq. cage ind. motor?
There are Two questions about Steam Turbine Generator... What is HRSG bypass of LP, HP used for in power generation? In particualar, in the event that fault of HP bypass, there would be STG TRIP in operation but none on the LP bypass fault...what's the reason ?
What the purpose of transient fault recoredr in substation
how calculate external illumintion in a compound area. for e.g. there is one open park having 600m2 area and i have to put 40w flouresent tube fitting with pole. how shall i calculate the numbers of fitting.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)