How Can we calculate the rating of a cable?Show the formula?
Answers were Sorted based on User's Feedback
Answer / prof. nazar m. karyar
VD = 2 x K x Q x I x D/CM - Single Phase
VD = 1.732 x K x Q x I x D/CM - Three Phase
“VD” = Volts Dropped: The voltage drop of the circuit
conductors as expressed in volts.
“K” = Direct Current Constant: This is a constant that
represents the direct current resistance for a one thousand
circular mils conductor that is one thousand feet long, at
an operating temperature of 75º C. The direct current
constant value to be used for copper is 12.9 ohms and 21.2
ohms is used for aluminum conductors. The “K” constant is
suitable for alternating current circuits, where the
conductors do not exceed No. 1/0.
“Q” = Alternating Current Adjustment Factor: Alternating
current circuits No. 2/0 and larger must be adjusted for the
effects of self-induction (skin effect). The "Q" adjustment
factor is determined by dividing alternating current
resistance as listed in NEC Chapter 9, Table 9, by the
direct current resistance as listed in 2. Feeders – This FPN
recommends that feeder conductors be sized to prevent a
maximum voltage drop of 3%. The maximum total voltage drop
for a combination of both branch circuit and feeder should
not exceed 5%. [215-2(d) FPN No. 2],
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shoebullah
with referance to prof.nazar
answer ... Cant we calculate
voltage drop by this formula
Vd= IZ
where Z= R*cos(pi) + X*sin(pi)
and R= r*1/1000, X=
x*1/1000 ......... I am
suggesting in this way also
we can find voltage drop of a
cable ....... And further we need
to calculate percentage of
voltage drop by this formula
%Vd= sq.root of 3 * Vd/VL
*100
where VL Is line voltage ... It
should be <3% for main
distribution board <5% for all
distribution board
Is This Answer Correct ? | 0 Yes | 1 No |
Do Phase angle measurement have any application in freq/harmonics measurement? If so how?
In synchronous motor, how the field current is related to armature current..i know its inversely proportional..but concept wise...i was nt clear....pls help me...
What is the criteria that generally follow by distribution licenses to fix contact demand of their industrial customers?
What is the effect of leading power factor for power transformer & D.G?
WHY TERTIARY OF POWER TRANSFORMERS IS LOADED WITH EQUIPMENTS LIKE CT,PT,ISOLATOR AND CB
What is the effect of impedance on the heat losses in case of AC system??? Does heat losses really depends on the impedance or depends only on resistive component only..??
how to calculate unit consumption on 3phase 380-415 v0lt kilowatt motor eg ( 55kw,380v,3phase 50-60hz)
Frequency of rotor emf in induction motor is around A same as stator frequency B 50% C 5 % or below D 30%
Why the tank of transformer is made rectangular not circular??
why dc power can not be used in transformer?
33 Answers GE, Sail,
what will happen at the time of CT saturation?and what will be the Relay's function at the time of CT saturation?
What is the stander resistance value between the neutral and earth?
10 Answers Crossdomain, Sepco,