Transmitter reading is zero but in DCS showing one Bar what is the reason ?
Answers were Sorted based on User's Feedback
Answer / atul bharadiya
in field measuring unit is BARG & dcs Unit is BAR A,means
gauge & absolute pressure
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / palanikumar
1. check the range LOW LIMIT in DCS . its may be more than one bar.
2. check the isolator or spiliters if anything between DCS and transmitter.
Is This Answer Correct ? | 0 Yes | 0 No |
how to know power plant process with corresbonding laws&thoeries
A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic meter/hr. Thorough impulse line flushing and zero calibration has been done, yet problem persists. What do you think is the problem and how do you rectify this fault?
Why we use 250 ohm resister in series hart communicator?
Why Current(Ampere) is chosen as Fundamental Quanties not Charge(coulomb) ?
what is the differnt between open loop and close loop ?
Whatis the reset ofset and control system in instrumentation
0 Answers Asyad International Company, CAE, Sugar Factory,
hello.my friends.i am an electronics & instrumentation engineer.i want to know Q1.why lugs use in instrumentation cable termination? Q2.if limit switch not working what to do?
What is an instrumentation amplifier? How is it better than a differential amplifier when handling outputs from a wheatstone's bridge?
Consider a level troll. i am getting a correct value in 4mA and 20mA. the value in the middle(30 to 60%)is disturbed and i am not getting the appropriate value. what is the solution to normalize the level and to get the correct value..
what do you mean by CJC (cold junction compensation).?
Is that Speed Probe and Vibration Probe sensors are same,if yes what is the diff b/w them?
what is the difference between 3,4 wire RTD sensor?
6 Answers HTA Instrumentation,