If i want use the 6 kg/cm2 pressure gauge then how to
calculate its pressure gauge range?
Answer / carl_ellis
The general rule of thumb is to put the working range in at
the mid-range of the scale of the pressure gauge.
Remember, a bourdon tube is damaged beyond repair when
overpressurized.
Alternative rules are
If the working Range is
- Steady: the working range can be 3/4 of full scale value
- Fluctuating: the working range should be 2/3 of full
scale value
- Full scale value: the gauge is working near its limit.
Short duration at full scale value is advised. Replacement
with a higher range gauge is advised.
Typical standard dual scale gauge dial ranges are shown below:
kg/cm2 psi
0-1.06 0-15
0-2.1 0-30
0-4.2 0-60
0-7 0-100
0-10.6 0-150
0-11.0 0-160
0-14 0-200
0-21 0-300
0-28 0-400
The 0-11 bar-Kg/cm2 range puts a 6 kg/cm2 working value just
above mid range.
Yeah, yeah, I know. 1 bar is not exactly 1 Kg/cm2 but we're
talking mechanical gauges here.
Carl Ellis
Measure First
Is This Answer Correct ? | 0 Yes | 0 No |
Explain, and give a real-world example of MODULATING control
what is the difference between mmhg & mmwc?. i want to calibrate a transmitter in the range of -100 to 300 mmwc. Which is the reference for calibrate the Tx,if mmwc not available?. Is it mmhg or mmho2?.
Decibel.
A pressure differential gauge type of instrument has a manifold with 2 isolation valves (hp and lp),2 vents(1 each for hp and lp) and 1 equalizing valve. Determine the position of each valve(either fully closed or fully open) when troboulshooting to: 1. zero the transmitter. 2. determine if there is a block in the impulse line. 3. determine if the gauge is functioning properly. The process fluid is water.
without color coding, without nameplate, without multimeter how can you find the type of thermocouple???
how flame detectors sense the flame.
hi everybody. right now i am working with thermal power plant. our company plant is tripped because of program corrupt. i would like to know is it possible when the plant is running. we are using FREELANCE ABB800F CONTROLLER.
What is the Difference between CNC and PLC
i want to measure temp of hot sand(welding flux) in closed chamber(around 150 deg C).Which is better thermocouple or thermometer?
how can be calibrate flow indication transmitter (rosemount) it shows excess milli amps nearly about 24 ma on full scale, but its scale was set on 20ma on full scale..???how can be simiulate..???
Calculate the maximum pressure drop that can be allowed to occur across a control valve, so that we can prevent cavitation / flashing from occurring. Use the following formula: Δ P allow = Km (P1 – PvapourA) where, Δ P allow - the maximum allowable differential pressure for sizing purposes, or terminal pressure drop; Km- the valve recovery coefficient from the manufacturer’s catalogue; P1 - absolute inlet fluid pressure; PvapourA - absolute fluid vapour pressure at the inlet temperature; Use Atmospheric pressure = 101.3 kPa, P1 = 1200 kPa(g), PvapourA = 4 kPa, KM = 0.72
can anybody will tell me abiut PID controller.