for 644KW load which MCCB should i use
Answers were Sorted based on User's Feedback
If i consider your 644kW load as a motor then,
I Assumed some parameters are:
644kW Motor, Power Factor - 0.9, Efficiency - 0.9, Load
Connected Voltage - 415V Then,
I = (644*1000) / (1.732*415*0.9*0.9) = 1106Amps
Considering 20% Margin = 1106 * 1.20 = 1327Amps
Conclusion:
So, We can choose Breaker rating is higher than that
1327Amps. Generally no one use the MCCB breaker above
800Amps. So, we can prefer the 1600Amps VCB Breaker for that
644kW Load.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / antaratara ghosh
assuming the load as motor,operating voltage as 415 V,pf
as .85, efficiency as .95,
rated current, Ir= (644)/(1.732*0.415*0.85*0.95)
= 1110 A (approx)
now considering VFD starting for the motor,
starting current, Ist= 2*Ir
= 2220 A
considering margin of 20%, maximum current flowing =
2220*1.2 = 2664 A
Since MCCB are not used above 630 A in India, you have to
go for 3150 A (which is just greater than 2664 A and
available in market) ACB...
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ahmed raza
Formulla for calculation of breaker is...
Total load in Watts/380(voltage)*0.8(pf)*1.732(delta to Y
conversion)
So
= 644/380*0.8*1.732
= 1223.10
we can say
= 1250AMPs breaker should be use....
| Is This Answer Correct ? | 0 Yes | 3 No |
200-100/1-1A – Transformer Knee point voltage
what is formula of dc current and resistance.
can any one know is sbi interview based on merit or based on roll number
why the rating of a transformer in kva not in kw.
I am working as a software engineer for the past 4 years. I am interested to do M.tech in premier inst. like IIT, IIIT, NIT,... I am preparing for the GATE exam for the past 2 years. Can anyone tell me how about the placement in IIT's for m.tech in (microelectronics and vlsi or electronics related discipline). Some of them are telling like placement is very rare for m.tech electronics. Also the placement details in IIT websites are not true. Is that so ? can any one help us regarding this.
explain the details about vaccum circut breaker and advantages?
Why strting torqe high in inducation motor?
fuses rated by amperes but not power,why?
difference between moore and mealy model
What is the range of efficiency of thermal or steam power plants? Why it is so low?
HELLO SIR, IAM PREPARING HPCL EXAMS. SO PLS SEND MATERIAL OF HPCL ELECTRICAL ENG..TO VIJAY_8888@YMAIL.COM
Please let me know when replacing electromechanical Relays for protection of generators with sr489 multilin Relay, then there is no need to use 86 master trip relay Too. I am wondering this multilin relay has no contact to Stop breaker reclosing as 86 does
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)