What is the difference between earth fault and restricted
earth fault protection?
Answer / m.gopinath
Earth fault protection is non-unit protection for earth
faults where as restricted earth fault protection is a unit
protection (ie differential protection of Y connected
alternator/transformer) for earth faults. So we can say the
Restricted earth fault protection is differential
protection of a y connected winding for earth faults only
but not for phase-to-phase faults.
Is This Answer Correct ? | 7 Yes | 1 No |
What is marx circuit?
Suppose an electric motor with a controller is not working. What is the sequence of testing you will do in your troubleshooting?
wat is the current produced in a 5000v megger? when the positive and negetive terminals are touched on our body get s shock?
What is the minimum distance to be maintained in between HT panel and LT panel and Instrument panel as per IEC and NEC standards?
Can I use 1 phase power supply to run 3 phase motor? If yes, how?
What is PQA???Applications........
What are the electrical engineer roles and responsibilities in chemical plant?
Determine the minimum cable size for a 28A single phase final sub circuit originating from the distribution board supplied by three phase submain. The route length of the final sub circuit is 54 m. Assume 1% voltage drop in the consumer's mains. Submain specification: Cable: 50mm2 4 core V75 copper; Route length 42m; Maximum demand 135A per phase
what is RCBO?
How to increase solar cell efficiency ?
if three phase supply is given to single phase transformer, what will happen?
Why the brushes used in dc machines are made of carbon not from other metal?