what is the minimum bdv value for 400 kva transformer?
Answers were Sorted based on User's Feedback
Answer / joseph vennel
There is no minimum value for BDV of a transformer oil. BDV of the oil represents the insulation level of the medium, in this case oil. More the BDV value the better. New Transformer oil has a typical BDV of 60 kV/mm.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / arun.r
bdv value depend upon voltage ratting
call 7389944985
Is This Answer Correct ? | 1 Yes | 4 No |
Clearly Define Active,Reactive,Apparant power.Which applications used which power above metioned power?
in electrical control panel. how can i choose the cable rating. (example - 11kw motor, 18-25A mpcb}
why is the rating of transformer done in kva and not in kw.
can any one provide me a connection wiring diagram for a DG set control panel along with BOM?
role of shunt coil in circuit breakers
how to calculate the bus-bar size. give formula with description
while we select CT, why the CT ratio is divided by 5?? ex:250/5,15VA,CLASS-1 CT.Why it is divided by 5??Help me please
i HP = ?? 746 watts or 735.5 and how??
in the Distribution system .which one is Most Economically used by Power Engineer ? a)3 Phase3 wire System or b) 3Phase -4wire System
how do you test tachos and servos
What is instrumental error?
A 10 kva ,400v/200V , single phase transformer with 10% leakage impedance draws a steady short -circuit line current of