Hello friends., my question is related to testing of current
transformer... A Ct having knee point voltage of 750 volts.,
and I have two step up transformer's of rating 230 v to
440 volts., can I obtain the value of 750 volts by using the
two transformer's.... If yes then how could I connect the
transformer's to obtain knee point voltage?? thank you in
advance
Answer / k.prakashchandra
Connect 230 V sides of trs in parallel with
dimmer-stat.Connect secondaries in series . Connections
should be done in such a way that the secondary voltages add
to each other.This can be ensured by measuring voltage .
Is This Answer Correct ? | 1 Yes | 4 No |
A MACHINE WHICH HAVE 1000rpm SPEED IS LARGER IN SIZE AS COMPARED TO THAT OF A MACHINE WHICH HAVE 1500rpm.WHY ?
any application of back emf
what type of euse we should use ? 1- High resistance & low temperature 2- High temperature low resistance
Why we should not parallel the with EB
what is the tolerance of electrical frequency for India? it's .5% or 1%?
Load break swicth maintenance procedure.
when ur using single phase type of load for a 3.5core power cable .Why neutral is .5 and how much current in the neutral if we consider neutral as a reverse path for three phases.
why current coil has less number of turns compared to pressure coil?
What is the one main difference between ups & inverter ? And electrical engineering & electronics engineering ?
We are having a 2000KVA DG set. It trips with Over speed and Engne Hot when the mahine is stopped in full speed. How shall I analyse the block load and reverse power.Is the problem related to power factor. The machine which runs on this DG is having all Synchronous motors with incividual Drives.
To attain a powerfactor more than .95, how much kvr should we use for 100 HP of current
4 Answers Bhel, Scooters India,
What makes the difference between 50Hz supply and 60Hz supply which one is economical? What is the use of using increased frequency?