What is the technical formula to calculate the load taken by a motor in Amperes ?
Answers were Sorted based on User's Feedback
Answer / anand_gupta112001
Amperes when horsepower is known
1) HP x 746/E x Eff x pf (for single phase)
2) HP x 746/1.73 x E x Eff x pf (for 3 phase)
Amperes when kilowatts are known
3) Kw x 1000/E x pf (for single phase)
4) Kw x 1000/1.73 x E x pf (for 3 phase)
Note: I = Amperes; E = Volts; Eff = Efficiency; pf = Power Factor; Kva = Kilovolt-amperes; Kw = Kilowatts
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / sureshkumar balakrishnan
In AC Single Phase: P=V*I*PF
In AC Three Phase: P=1.732*V*I*PF
In DC: P=V*I
P(KW)=Load or Power, V=Voltage, I=Current, PF=Power Factor.
Is This Answer Correct ? | 0 Yes | 1 No |
What is the specification of service line (ie from electrical post to cut out) used by electricity boards used in india.i mean which material,its size etc.. please give the answer at lalkishan.p@gmail.com
What is the use of 1:1 isolation t/f in any circuit...?
why corona loss is less with negative polarity?
Explain the difference between verilog task and verilog function?
what is vector surge & vector shift? we have 25.3 MW(11kv) generator & 11kv/132kv transformer, connected with with 132 kv grid.vector surge relay is tripping frequentaly.what is permissible maximum limit for this.
why substation ratings are multiple of 11 means 11\33 kv substation
What is meant by turbo alternators?
What is meant by Low Resistance Cable and High Resistance Cable.
What is Load sharing of Transformer ?
capacitor is load free component but why ampare meter shows current when capacitor bank breaker close?
what is the method to measure the transformer current carrieng capacity in three phase.
what is the difference between dry and wet type of 132kV terminations. which one is durable