how to calculate the knee point voltage of current transformer?..

Answer / manisand1


CT resistance = 1.8ohm,
Lead resistance = 4.0 ohm,
Starting current = 195*5/200 = 4.875 Amp
Starting voltage = 4.87(1.8+4)= 28.275 = 28.3 volts
This is to be set to 30Volt,

But please remember that knee voltage should be 60 volt
minimum.

For anymore clarification you can mail me to :-
manisand1@hotmail.com

Is This Answer Correct ?    1 Yes 1 No

how to calculate the knee point voltage of current transformer?..

Answer / puneet prashar

Knee Voltage=2X Earth Fault current(RCT + RW)/CT
Trasformation ratio

Where
RCT= CT impedeance as per manufacture1.02
RW = Wire resistance as per manufactre
say.oo32/metre then RW= 2X 200mtr X .0032

CT transformation ratio= 4000/1=4000
4000/5=800

VKnee= 2X58000(1.02+1.28)/4000 or 800 depending upon ct used

Vknee= 66.7v

Vknee> relay stability Voltage

Relay stability voltage formula will be given by relay
manufacturer as every relar manufacturer has their own formulas

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Which Kind of machines(in terms of poles) give the smoothest DC

0 Answers  


if the stetor speed (N S) increase by 20% then the rotor speed will be increased by 20% is it true. ?

4 Answers  


WHAT IS THE REASON OF CHANGE FREQUENCY IN DG SET AFTER FULL LOAD.

1 Answers  


How many energy meters can be connected on a 15VA Voltage transformer. please send a calculation sheet.

0 Answers  


can motors working at parallel operation like D.G set and transformers? It means asking about two motors coupled with same load???

1 Answers  






what is the safe meggar values for motor, transformer HT, LT and Cables? IF we want to replace I/C bay at our 220 kv substation which is of 140 mw load capacity bay to be replaced by 400 mw capacity bay.other than CT(1200/1) what are the other equipment i have to replace. why we generally use 3.5 core cable or in other word 1/2 core for neutral and also confirm me that in balance conditiob(3 phase)current in neutral will zero

0 Answers   Jindal,


What is superposition theorem?

0 Answers  


why inductance is not present in a incandescnt lamp?

2 Answers  


how to prepare the technical test

0 Answers   RRB,


What is the Power factor of DC Power system ?

9 Answers  


what is F.A.P in fire alarming system?

3 Answers  


ups battery design formula

0 Answers   Amara Raja,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)